Just upgraded a domestic property today new consumer unit e.t.c now I've installed new earth spike with 16mm earth. Provided 30ma rcd protection for all final circuits, Ze readings are 25.2 ohms which is well below 200 ohms, Zs reAdings on final circuits are very high in the region of 30 ohms is all sounds well to me anyone else got any info to help me get better readings or should I just leave it as rcd protects up to 1667 ohms
 
Fair point I will investigate tomorrow as I've not done full test as yet, as it's a void property
so...if you had done the tests properly (in sequence)...then you may/will have found high values of (R1 R2)..

how come all Zs values are in the region of 30 ohms?..

get end to ends on rings for a start...then do the calc for expected (R1 R2).....
 
I've just re tested Ze and pfc values I got

L-e 25.2 ka 10
L-n 0.11 ka 2.2

I'm pretty sure this system may already be converted to pme but the property hasn't ever been upgraded and just requires earth conductor to connect into incoming neutral obviously I can't do that
 
your Zs readings should not be 5 ohms higher as the bonding will bring them down 9 parallel earth paths). as i said earlier, check at L busbar to E. internal resistance of RCDs, MCBs and main switch can affect the readings.
 

Reply to TT system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
969
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top