D

dal_87

Hi doing a cu change at weekend 8 way dual rcd on a 100amp fuse and first time doing one on a tt system noticed that main bonding looks to be a 6mm and so is bonding to gas and water looked at some posts and people say is ok but regs state 16mm main earth and 10mm bonding do I change it all and follow regs book as I should do or is earthing ok as it and will I affect it if I upgrade earthing size. Also are the 16 mm tails fine ? Thanks
 
with TT earthing systems, the fault current is relatively low and so it's common to have a MEC of only 6mm. if you check your regs. the 16mm for TT is the requirement if it'd buried without protection. also, you need to replace the main switch with a 100mA time delay RCD as you will not otherwise meet disconnection times. the 16mm tails will be fine if they show no signs of damage.

edit: the bonding conductors will also be OK if sound and give decent resistances.
 
with TT earthing systems, the fault current is relatively low and so it's common to have a MEC of only 6mm. if you check your regs. the 16mm for TT is the requirement if it'd buried without protection. also, you need to replace the main switch with a 100mA time delay RCD as you will not otherwise meet disconnection times. the 16mm tails will be fine if they show no signs of damage.

edit: the bonding conductors will also be OK if sound and give decent resistances.

Why ? ? ?
 
An expensive and unnecessary back up.

I think this must be the first time i've disagreed with you about something!

Modern RCDs just aren't reliable, they need their test buttons pushed regularly to keep them working and people just don't do it. I'm sure in a few years time we'll be seeing the cheap and cheerful RCDs in cheap dual RCD boards failing on EICRs on a regular basis.

For some reason that all important sticker which tells you to push the test button regularly just doesn't have the desired effect.
 
Yes new one is insulated .....the board iam taking out is an old rewireable fuse board with a 30year 100ma rcd in front of main switch which saved the house from catching on fire the other day so done its job well after all this time. Great dual cu fine ! but what if I need a feed to garage rcd cu in swa normally I try not put this on house rcd but in this situation will have to ?
 
I think this must be the first time i've disagreed with you about something!

Modern RCDs just aren't reliable, they need their test buttons pushed regularly to keep them working and people just don't do it. I'm sure in a few years time we'll be seeing the cheap and cheerful RCDs in cheap dual RCD boards failing on EICRs on a regular basis.

For some reason that all important sticker which tells you to push the test button regularly just doesn't have the desired effect.

I’m not going to disagree with you but a 30mA and a non-time delayed 100mA in series isn’t going to show much discrimination unless it’s low level cumulative leakage. Under fault conditions it will be a ---- up which goes first.

As for being more reliable, some were, some unfortunately weren’t. The Hackbridge Faraday AKA Wylex 100mA were a pain in the bum.

As for the label, I‘ve told you before, you’re got getting anywhere near my CU!

(OP, it’s a long standing joke about my hatred of labels plastered all over CU’s)
 

Reply to TT system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
665
loz2754
L
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top