Could some one help me?

What readings should you get when installing new circuits for TT systems?
I am aware that you have to get a reading for the earth rod but what should you have for the following Ze and Zs.?
 
Ze for TT system should be under 200 ohms. as your Zs reading will be far higher than max. allowed for disconnection times to be met, fit RCD/RCBO to all circuits.
 
:eek:Thanks for that.

So if the readings Ze was 15 ohms at the earth rod and the installation has a 100mA main RCB protecting the whole installation, what would you suggest I should tell the client.
 
he should have, apart from the 100mA RCD, 30mA RCDs or RCBOs on all circuits. end of story.
 
best way to configure the board is to use the 100mA RCD as main switch and fit 2 additional 30mA RCDs, split board. if this is not practicable, due to space, then RCBO each circuit. expensive but the ideal way as tripping of 1 cct. will not affect any other ccts.
 

Reply to TT Systems and Ze and Zs readings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
192
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
512
  • Question
That 'stranded 2.5mm' was probably imperial 7/.029 which is about 2.9mm2. Which might account for expected readings being different.
Replies
6
Views
429

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top