I recently changed a fuse box and began testing to discover the property has no earth. I put an earth rod down and my Ze is 49ohm, which is an acceptable figure according the the 17th, which requires less than 200ohm. How do my Zs readings work? I am measuring about 12ohm on the socket circuits. All circuits are RCD protected. Do I just accept these high readings compared to TN systems, is this normal? Another question I have is what size earth cable should be used?

This is only the second time I have installed an earth rod, the first being for a temp supply.

Regards,
GrantM.
 
It's a joke really isn't it, the same with
The DNOs clips on the main fuse and meters, there is books and books of regs about saftey we join a part p scheme to prove we work saftley yet the DNO (in most cases) have not provided a safe way of the contractor being able to install a new board.
 
Another question I have is what size earth cable should be used?

This is only the second time I have installed an earth rod, the first being for a temp supply.

Regards,
GrantM.

With respect to the earth size, the OSG and regs are open to interpretation and you could fit 6mm but I always use 10mm because I've always got that to hand and as you'll probably be upgrading the bonding too its easy to use the same throughout.
 

Reply to TT systems??? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
164
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top