Hi all,just started using this forum,amazed theres so many people on it.

I have to change a board on a TT system(haven't done one before).
The cpc looks to be around 6mm(not sure untill i test it wether to change it to a 16mm),and has an old rccb protecting a wylex db.

Can I use a 17th dual rcd board or do I have to use a normal board with rcbo's?
Also am I right in saying that the Ze has to be below 200 ohms and the Zs for each circuit 1667 ohms.

Appreciate any advice

Thanks All
 
Welcome along.
:D
As this is the introductions thread, try posting your querey in the relevant section of the forum.

You will get more views and replies there.
 
Do you mean the main earth looks to be 6mm??
If so and it is not burried in the ground it is probably ok. 16mm if burried.

Yes you should aim for your Ze or rod Ra to be as low as poss.
Although the regs state that for a 30mA Rcd the max is 1667.

You could fit either db, I would be tempted to replace the main switch in either with a 100mA type s Rcd. (Time delay) for extra protection. Not required.
Personally rcbos is a better job but a lot more money.

Hope this helps
 

Reply to tt systems in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
763
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
765

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
376
Thanks I re tested this morning as I had other bits to finish off . I tested three times and it was 0.30 every time . It may have been my leads...
Replies
7
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top