Hi. Its my first week on a new job and we're having a debate about the use of TT systems.

eg. You have a 2 bed detached house which is on a tnc-s system and you hand a detached garage supplied from the house, from the house db.

how would you earth the garage supply?

Thanks
 
extend the TNC-S to the garage. bear in mind that any extraneous metal parts in the garage will need to be bonded back to the house MET in 10mm.
 
Hi. Its my first week on a new job and we're having a debate about the use of TT systems.

eg. You have a 2 bed detached house which is on a tnc-s system and you hand a detached garage supplied from the house, from the house db.

how would you earth the garage supply?

Thanks

Hi mate
Dont know which side of the 'debate' you are on ,but for the non-exporting of pme handwringers please find the regulation which forbids it before starting a 'debate'...:snore:
 
There is a sticky thread on one of the sites forums, It covers this subject ad infanitum. To save a lot of people typing look for it!
 
Oh no,the exporting pme question has reared its ugly head once again :21:

This must surely stimulate the"how to wire the shed" terrorists:hurray:


:33:
 

Reply to TT systems. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
106
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
905
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K
Agreed, i have a cabin in the woods, water heating and hob is via 19Kg propane bottles, lasts ages and space heating is via warm air heaters via...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top