Hi all,
My first post here after an exceedingly long time reading and studying this encyclopaedia of a fourm.
I had a job in on sunday night which was leaving the whole house in darkness the second the shower was turned on.
TT installation with front end RCD to cover every circuit.
Tested RCD - Fine
IR tested (shower) - Fine
IR test wiring - Fine
Ze = 85 - (decent for a TT)
Zs at socket next to board 0.7
The conclusion being the bonding to the water was stealing the benefits of next doors TNCS but the clash of two earthing systems was causing the trip. I quickly disconnected the bond at the pipe to test the theory and voila shower working perfectly no tripping.
Here's the question. Is there any requirement to bond back onto this water pipe when it caused this problem in the first place. If it had been plastic (or even gets changed to plastic later) it would not be necessary.
All other bonding is OK or mostly not actually required as the majority of the plumbing is in plastic polypipe and resistance to MET is hugely over 25Kohms at the nearest touchables, which in this case is a short length of copper pipe in between plastic pushfits housing the isolator valve.
The house is now fully back to TT , safe and not tripping but I thought I'd kick it around on here to get your views. Something always crops up worth knowing.
Lastly the house is up for tenancy but not yet occupied and hasn't had a full test yet so if it turns out removing the bond was for some reason a dozey idea, we have plenty of time to put it back again.
Thanks in advance.
My first post here after an exceedingly long time reading and studying this encyclopaedia of a fourm.
I had a job in on sunday night which was leaving the whole house in darkness the second the shower was turned on.
TT installation with front end RCD to cover every circuit.
Tested RCD - Fine
IR tested (shower) - Fine
IR test wiring - Fine
Ze = 85 - (decent for a TT)
Zs at socket next to board 0.7
The conclusion being the bonding to the water was stealing the benefits of next doors TNCS but the clash of two earthing systems was causing the trip. I quickly disconnected the bond at the pipe to test the theory and voila shower working perfectly no tripping.
Here's the question. Is there any requirement to bond back onto this water pipe when it caused this problem in the first place. If it had been plastic (or even gets changed to plastic later) it would not be necessary.
All other bonding is OK or mostly not actually required as the majority of the plumbing is in plastic polypipe and resistance to MET is hugely over 25Kohms at the nearest touchables, which in this case is a short length of copper pipe in between plastic pushfits housing the isolator valve.
The house is now fully back to TT , safe and not tripping but I thought I'd kick it around on here to get your views. Something always crops up worth knowing.
Lastly the house is up for tenancy but not yet occupied and hasn't had a full test yet so if it turns out removing the bond was for some reason a dozey idea, we have plenty of time to put it back again.
Thanks in advance.