a 6mm copper conductor, 70 degrees, protected by a 45a 1361 fuse, with a fault current of 240a, will the fuse trip in time to protect the cable?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss tuesdays 2391 20 question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
i got 12 sec with the disconnection time (sic)6 sec. so yes. just thought id put it out there.
i made k as 148 other than that im the same
where from?
Reply to tuesdays 2391 20 question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net