J

jase

have calculated mx demand to be 60A with diversity
1x32 ring
1x16 radial supply to hand 3kw hand wash unit
1x 6A lighting circuit

gonna put 63A 30mA main breaker in 5 way fuseboard fed by 10mm 2 core swa and TT it
swa run would be 35M from house.
would it be advisable to put this on an mcb in the house cu? 63 a breaker?
or which i think is better option, spilt tails in henley block, earth armoured in MET and out 63A switched fuse in?

been reading alot of posts on here and seems there are alot of 63A 30mA boards being fed by 40A mcb, how so?
 
have calculated mx demand to be 60A with diversity
1x32 ring
1x16 radial supply to hand 3kw hand wash unit
1x 6A lighting circuit

gonna put 63A 30mA main breaker in 5 way fuseboard fed by 10mm 2 core swa and TT it
swa run would be 35M from house.
would it be advisable to put this on an mcb in the house cu? 63 a breaker?
or which i think is better option, spilt tails in henley block, earth armoured in MET and out 63A switched fuse in?

been reading alot of posts on here and seems there are alot of 63A 30mA boards being fed by 40A mcb, how so?

actually max demand is less than 60A due to lighting circuit but only marginally
 
As you've said, split the tails, feed into a new MC 60A switchfuse to supply your new office with a new DB in the office.


If TN-S system then no need to TT it at all, if TN-C-S again no need for TT but other criteria must be satisfied so may be easier in this instance to TT it.
 
Last edited by a moderator:

Reply to turning outbuilding into office in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top