I have done a little research on my question, but most of the previous threads are 2010 or older, and this issue somewhat different to current ones (I think!). I'm new to the 17th and still learning.
I went to a potential job today, to have a look at a job for a (friend) plumber. It's a large 5 bedroom house, and the work is on converting an existing bedroom to a bathroom, therefore all work notifiable. However on inspection of the CU I noticed a potential problem. The house had an integral garage, that has been converted into a living room. The then CU had been moved to a cupboard of the living room. I saw that the CU had been fed from a 100amp fuse/isolator (where the old CU was) with a 16mm 6242y cable (meter tails). The main protective bonding conductors are 6mm 6491x. The meter tails are in excess of 3m. The CU is 17th edtion 12 way split load with a 100amp isolator. I have not calculated the max load, but lets be generous and say 80amp. The cable is proably clipped direct in the joists of the room above.
I know I will be told to do my cals, and I will (when I have time), but I'm thinking the cable is underated, 87amp (if clipped direct, not sure about insulation). From my OSG, for TN the earthing conducter should be 10mm for a 16mm line conductor (16mm 6242y is 6mm cpc).
My thoughts are that I could derate the consumers isolator to 80amp to allow for discrimination, but potentially the cable will be at less than 50mm in the floor void (requiring RCD protection), and the cpc is too small to act as the main earthing conductor. I could just walk away, but my (friend) plumber bought in the previous electrician. So before I state my case...am I right in what I'm saying?
I went to a potential job today, to have a look at a job for a (friend) plumber. It's a large 5 bedroom house, and the work is on converting an existing bedroom to a bathroom, therefore all work notifiable. However on inspection of the CU I noticed a potential problem. The house had an integral garage, that has been converted into a living room. The then CU had been moved to a cupboard of the living room. I saw that the CU had been fed from a 100amp fuse/isolator (where the old CU was) with a 16mm 6242y cable (meter tails). The main protective bonding conductors are 6mm 6491x. The meter tails are in excess of 3m. The CU is 17th edtion 12 way split load with a 100amp isolator. I have not calculated the max load, but lets be generous and say 80amp. The cable is proably clipped direct in the joists of the room above.
I know I will be told to do my cals, and I will (when I have time), but I'm thinking the cable is underated, 87amp (if clipped direct, not sure about insulation). From my OSG, for TN the earthing conducter should be 10mm for a 16mm line conductor (16mm 6242y is 6mm cpc).
My thoughts are that I could derate the consumers isolator to 80amp to allow for discrimination, but potentially the cable will be at less than 50mm in the floor void (requiring RCD protection), and the cpc is too small to act as the main earthing conductor. I could just walk away, but my (friend) plumber bought in the previous electrician. So before I state my case...am I right in what I'm saying?