Hi all, can someone clarify for me if it is acceptable to run a Twin and CPC sheathed cable to an outhouse. There is an existing alcathene duct in situ, which runs under a patio with an existing supply cable already in place.
Job has not commenced but the question has been raised. I have only ever used SWA so have never given it much thought.

Cable clearly does not have an earthed metallic sheath but is well protected against mechanical damage

Many thank`s
 
Think you answered your question in the last paragraph , answer is no , it should be SWA, PVC is prone to rodent attack , water , uv rays etc
 
IMO if the duct provides adequate mechanical protection for the cable, no rfeason why T/E can't be used. SWA is preferable though for longevity.
 
I'd always use SWA, especially after seeing an idiot with a mini digger go through the mains gas supply to one of my neighbours house when digging a trench for drains.
 
As Spin has stated, yes it is acceptable, providing there is mechanical protection afforded where required throughout it's length. As for rodent attack, ducts should be sealed at each end after cables have been drawn in. Personally i would prefer to use a SWA cable, when installing a sub-main, especially when part of the cable run passes thru exterior space from the main supply location....
 

Reply to Twin and CPC to outhouse in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

I’m sure I’ve seen an LSF round cable used on sites before as well with an insulated earth. Not flex, something a bit more substantial but not FP...
2
Replies
21
Views
3K
I hate it when a shed is TTd, why can they not be extended from the tn system? popcorn ready
Replies
7
Views
670

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top