Hi Guys,
I'm currently studying for my C&G qualification and I was asked by my Dad about his new double oven and induction plate.
One of the Ovens is 2.2kW and the other is 2.8kW, also the induction plate is 440W. All appliances have 13A fused plug.
If I apply Diversity to the whole setup
I get 5440/230v = 23.65 amps
10a + (0.3 * 13.65) + 5 = 19.1 amps
Could you have two radial circuits of 2.5mm cable. One to run the 2.8kW oven and one to run the 2.2kW oven and the induction plate?
Would these then be attached to two 20A MCB's?
What sort of fused connection unit would you use?
Thanks for any insight you can give