MvP Electrics

hi everyone,

i went back to a job that i previously changed a consumer unit and certified. and i have noticed the builders/kitchen fitters have attached two 3.5kw ovens to a 32amp mcb 3 socket ring circuit wired in 2.5mm twin and earth. i have told the client. what else can i do? help grately appreciated.

thanks
 
if they knew they were getting electric ovens why didnt they ask you to pull a 6mm feed in whilst you done the new board. and how have they connected the ovens
 
Theres not much you can do . As this is a kitchen it should have a dedicated cooker circuit as there are limits on cookers etc in ring circuits not exceeding 2kw which sould be on a radial. Have they been hard wired ? If so they have altered your circuit and it nothing to do with you. Write a letter to Home owner / builder explaining this and potential mcb tripping due to overload and keep a copy with your certification. Show it to your accessor next time. If they have problems they will probably call you back.
 
hi everyone,

i went back to a job that i previously changed a consumer unit and certified. and i have noticed the builders/kitchen fitters have attached two 3.5kw ovens to a 32amp mcb 3 socket ring circuit wired in 2.5mm twin and earth. i have told the client. what else can i do? help grately appreciated.

thanks


Was the LABC notified by the kitchen fitters, bet they didn't notify so why not inform them to the LABC.
 

Reply to two 3.5kw ovens in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
427
  • Question
Thanks so much for all the responses guys! It seems that what I'm planning is nothing unusual or regs-busting. I'll hook it all up and have a...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top