Spudnik

Hi all,

Went to look at a job today that needs a little fettling.

Set up is.

House (very old) with meter situated on the first floor landing.

From here we have 25mm tails to a dp service block, with two 16mm T&E's, one going to a CU in the same cupboard, which feeds various circuits in the loft conversion.

Second drops down stud wall to the under-stairs cupboard to an old wylex which does the rest of the 'existing' house.

Can anyone see any reason why i cannot replace these with a standard CU with RCD main switch for each one, rather than dual RCD for both?

Much obliged.

J
 
can't see a problem with that. if 1 board is only , say a 4/6 way, you could consider RCBOs for better separation.
 
Cheers Tel,

I was thinking that however, its a Proteus CU and they only do 2 mod RCBO's that i could find and so they wont fit.
 
314.1 and 2 require that every installation should be divided into circuits as necessary to avoid danger and minimise inconvenience in the event of a fault. Designers are required to reduce the possibility of unwanted RCD tripping due to excessive protective conductor currents but not due to an earth fault.

I see this can be achieved in one house with two DBS.
Or as tel says rcbos if the customer wants to pay a little bit more for a far better set up lol
 
Jason, is the 16mm T&E that runs inside the stud wall mechanically protected in any way as I'm assuming it will not be RCD protected? I'm also assuming that the run is less than 3M as it is straight off the splitter block.
Apologies if I have the wrong end of the stick.
 
314.1 and 2 require that every installation should be divided into circuits as necessary to avoid danger and minimise inconvenience in the event of a fault. Designers are required to reduce the possibility of unwanted RCD tripping due to excessive protective conductor currents but not due to an earth fault.

I see this can be achieved in one house with two DBS.
Or as tel says rcbos if the customer wants to pay a little bit more for a far better set up lol

When does dividing circuits extend to dividing into sub-mains in a standard size house?? lol!! The Reg your quoting, is basically stating that you shouldn't have too many circuits being covered by a single RCD where accumulated natural leakage can give rise to nuisance tripping... It certainly doesn't mean install another CU/DB!!

All this lazy electrician has done, is supply an un-needed sub-main CU to cover a tiny roof conversion that probably could have been adequately covered by extending existing circuits on the first floor!!
 
Jason, is the 16mm T&E that runs inside the stud wall mechanically protected in any way as I'm assuming it will not be RCD protected? I'm also assuming that the run is less than 3M as it is straight off the splitter block.
Apologies if I have the wrong end of the stick.


Yes, i did miss out the part where i would also install a switch fuse before the DP service block.

When does dividing circuits extend to dividing into sub-mains in a standard size house?? lol!! The Reg your quoting, is basically stating that you shouldn't have too many circuits being covered by a single RCD where accumulated natural leakage can give rise to nuisance tripping... It certainly doesn't mean install another CU/DB!!

All this lazy electrician has done, is supply an un-needed sub-main CU to cover a tiny roof conversion that probably could have been adequately covered by extending existing circuits on the first floor!!

You are correct, however, it does not state how the division of circuits is achieved

I like that as well, best solution all round.
I found one house that had two single RCD boards one in the front hall, one in the living room, thought it was OK.

Indeed, and that is what i proposing to do.
 
I have just done a EICR on a bungalow that had two boards in, both with rcd as main switch. Basically, they had some work done (bedroom in loft space) and the electrician fitted an new board for the excisting install with rcd main switch and a new board for the loft with lights and ring main on it, this also had rcd main switch. Now the sparkys did one without giving the client an EIC and so when the LABC asked for one, they were knackered. So, they asked me. I said I could only do an EICR (100%) on the install and they would have to ask the LABC if this would be ok....anyway I did the EICR and as far as I know, the LABC didnt have a problem with two boards in one dwelling, both with rcd main switch's.
Hope this made sense, Ive been out for a few games of snooker and Ive had a few...........




Jay
 
I have just done a EICR on a bungalow that had two boards in, both with rcd as main switch. Basically, they had some work done (bedroom in loft space) and the electrician fitted an new board for the excisting install with rcd main switch and a new board for the loft with lights and ring main on it, this also had rcd main switch. Now the sparkys did one without giving the client an EIC and so when the LABC asked for one, they were knackered. So, they asked me. I said I could only do an EICR (100%) on the install and they would have to ask the LABC if this would be ok....anyway I did the EICR and as far as I know, the LABC didnt have a problem with two boards in one dwelling, both with rcd main switch's.
Hope this made sense, Ive been out for a few games of snooker and Ive had a few...........
Jay

Just goes to show the standard of electricians these day's, or i should more correctly say, DI trained persons!! lol!!
 
When does dividing circuits extend to dividing into sub-mains in a standard size house?? lol!! The Reg your quoting, is basically stating that you shouldn't have too many circuits being covered by a single RCD where accumulated natural leakage can give rise to nuisance tripping... It certainly doesn't mean install another CU/DB!!

All this lazy electrician has done, is supply an un-needed sub-main CU to cover a tiny roof conversion that probably could have been adequately covered by extending existing circuits on the first floor!!

Unless I'm reading jasons OP wrong the loft conversion CU is in the same cupboard as the meter....it is the existing circuits CU which is remote downstairs. There are a multitude of reasons why a separate CU for the loft conversion may have made sense to the original installer....(heavy loads added to the 16mm submain..shower?....existing circuits not suitable for extending?)....because of your illogical hatred of more than one CU in a dwelling you jump in all guns blazing without knowing the circumstances.
 
Last edited by a moderator:
It's anything BUT the best solution!!

Why?

Unless I'm reading jasons OP wrong the loft conversion CU is in the same cupboard as the meter....it is the existing circuits CU which is remote downstairs. There are a multitude of reasons why a separate CU for the loft conversion may have made sense to the original installer....(heavy loads added to the 16mm submain..shower?....existing circuits not suitable for extending?)....because of your illogical hatred of more than one CU in a dwelling you jump in all guns blazing without knowing the circumstances.

Indeed, you are correct wp.

There is no shower upstairs, purely a couple of rooms and a wc.

No, its not ideal, however, the installation will not be left any worse that it was originally.

I am all for sticking rigorously to the regs, however, common sense also has to be applied.



Now, of course with the submain, this will be split concentric and will be run inside a stud wall from top to bottom within 150mm of the corner.

Therefore, of course, as it will be less than 50mm from the surface will need to be RCD protected.

With that in mind, i am considering installing a 80A 30mA RCD in the meter cupboard to protect this, which will mean that the downstairs CU will just be a standard 8 Way with a main switch.

Alternatively, i could always run in down it the corner of the stairwell, external of the stud wall and box it in as they are yet to decorate.

Hmmm.
 
When does dividing circuits extend to dividing into sub-mains in a standard size house?? lol!! The Reg your quoting, is basically stating that you shouldn't have too many circuits being covered by a single RCD where accumulated natural leakage can give rise to nuisance tripping... It certainly doesn't mean install another CU/DB!!

All this lazy electrician has done, is supply an un-needed sub-main CU to cover a tiny roof conversion that probably could have been adequately covered by extending existing circuits on the first floor!!

Yes E54, it isn't the best solution I agree. But all I said was it could be achieved this way. Although now reading that the submains or concealed in a wall, they will require Rcd if not mechanically protected(unlikely)
So you would have no division would you??
I would say rcbos every time.
And find out exactly how the subs are installed.
Also re reading, there is no OCPD for them currently?
 

Reply to Two Cu's in One dwelling. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
265

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top