I'd appreciate any suggestions on this one. Went to job that was "socket not working" and quickly found loose neutral - owner had installed new faceplate.
Fixed the neutral problem, however, when testing I got a very high ELZ reading at that socket - this must have been an existing problem, as CPC connection on socket was fine.
I got the very high ELZ reading at one other socket.
Started to check all sockets on ring and found a number with loose terminations. Fixed all these, and replaced a couple of sockets, but higher ELZ at the two sockets remained.
Checked at board doing dead tests and we see the lose of continuity in CPC there.
So it sounds like a CPC break or partial break between sockets - but to get a bad reading on two sockets there would have to be two separate CPC breaks? So we can't split the ring into two 20A radials - need to find the breaks.
Before we start lifting flloor boards I wondered if I'm missing something obvious here - something that someone out there can point out? I'm hoping for a Doh! moment....
Fixed the neutral problem, however, when testing I got a very high ELZ reading at that socket - this must have been an existing problem, as CPC connection on socket was fine.
I got the very high ELZ reading at one other socket.
Started to check all sockets on ring and found a number with loose terminations. Fixed all these, and replaced a couple of sockets, but higher ELZ at the two sockets remained.
Checked at board doing dead tests and we see the lose of continuity in CPC there.
So it sounds like a CPC break or partial break between sockets - but to get a bad reading on two sockets there would have to be two separate CPC breaks? So we can't split the ring into two 20A radials - need to find the breaks.
Before we start lifting flloor boards I wondered if I'm missing something obvious here - something that someone out there can point out? I'm hoping for a Doh! moment....