Evening all, been a long time since I posted on here but I could use some advice if there's any going!

I've been asked to provide an EICR for a small building we look after for our client under contract. We are all done physically on site, but I've hit a snag filling out the report itself, in particular with Section L - Particulars of Installation at the Origin.

There is a small cupboard with the supply cable / cut-out / meter. The tails travel from the meter into an insulated adaptable box, and two pairs of tails come out, each pair feeding it's own three-phase x 8-way D - 24 circuits per DB / 48 circuits for the whole building.

Each DB has an RCD as a Main Switch - historically the supply to DB2 was taken out of DB1 as a sub-main supply. However due to problems with the 100A RCD main switch for DB1 tripping almost daily due to overload, due to it carrying the load for both DB's, we decided to put DB2 on its own supply from the meter a year or two ago.

This solved the overload problem, but now I have a problem filling out the details of the Main Switch - under the new configuration, there is, I would suggest no Main Switch as such - at least, there is no longer a single switch that can isolate the whole building / installation.

So is it a case of writing N/A in the boxes because there is no main switch?

Also, does the lack of a main switch breach BS7671? Should it be coded in Section F and if so how should it be coded?

Any advice would be gratefully received...

Thanks

Ben
 
I would record the principle db as having main switch and maybe on the schedule of results for db2 record the isolation method on there. I stopped over thinking these things and now make free use of the comments box. Especially is using niceic forms.
 
I would also specify the installation as having no single point of isolation and therefore no main switch to specify in the origin of the installation. However the main switch for each DB can be entered in the schedule of test results.
I tend to think that no single point of isolation when the DBs are all in the same location is not too critical and would specify it as a C3 improvement recommended, since it is clearly required with no ambiguity in BS7671. If there were widely separated DBs with no single point of isolation this becomes more dangerous and may attract a C2. In your case it is an easy resolution to fit an isolator at the adaptable box position.
 
Evening all, been a long time since I posted on here but I could use some advice if there's any going!

I've been asked to provide an EICR for a small building we look after for our client under contract. We are all done physically on site, but I've hit a snag filling out the report itself, in particular with Section L - Particulars of Installation at the Origin.

There is a small cupboard with the supply cable / cut-out / meter. The tails travel from the meter into an insulated adaptable box, and two pairs of tails come out, each pair feeding it's own three-phase x 8-way D - 24 circuits per DB / 48 circuits for the whole building.

Each DB has an RCD as a Main Switch - historically the supply to DB2 was taken out of DB1 as a sub-main supply. However due to problems with the 100A RCD main switch for DB1 tripping almost daily due to overload, due to it carrying the load for both DB's, we decided to put DB2 on its own supply from the meter a year or two ago.

This solved the overload problem, but now I have a problem filling out the details of the Main Switch - under the new configuration, there is, I would suggest no Main Switch as such - at least, there is no longer a single switch that can isolate the whole building / installation.

So is it a case of writing N/A in the boxes because there is no main switch?

Also, does the lack of a main switch breach BS7671? Should it be coded in Section F and if so how should it be coded?

Any advice would be gratefully received...

Thanks

Ben
 
Hi,just out of interest,how did the RCD letting go,become an overload issue?
Or do you mean "over-leakage"?
 
I disagree, historically it was one installation and still is as there is only one source of supply. By rerouting the supply for DB2 you have created two means of isolation not two installations.
I don't disagree, but IET Guidance Notes specifically state that they can be considered to be separate installations and therefore don't need a common isolator.
 
I don't disagree, but IET Guidance Notes specifically state that they can be considered to be separate installations and therefore don't need a common isolator.

If it is worded "can" be considered to be separate, then surely you can consider it otherwise too ?
"Must" or "Should" would indicate differently though.

I always define an installation by the incoming supply myself. My choice based on the vague definition of "installation" in the regs.
 
I've got one ...an old church 3 ph intake to various single ph supplies, all fed from connection blocks. Tails to local boards and switches with pyros and swa's out to remote boards.
No way can they afford to pay for a main switch and busbar chamber job......plus there's no room to fit it anyway.
NIC bloke's coming later in the month so I might just give it a mention to get him thinking and see what he comes up with...and waste a bit of time.
edit. Wonder if he'll recommend a failure......and shutting them down? ;)
For me it's a note saying individual isolation incorporated on db schedules.
 
Last edited:
I've got one ...an old church 3 ph intake to various single ph supplies, all fed from connection blocks. Tails to local boards and switches with pyros and swa's out to remote boards.
No way can they afford to pay for a main switch and busbar chamber job......plus there's no room to fit it anyway.
NIC bloke's coming later in the month so I might just give it a mention to get him thinking and see what he comes up with...and waste a bit of time.
edit. Wonder if he'll recommend a failure......and shutting them down? ;)
For me it's a note saying individual isolation incorporated on db schedules.

I think Richard Burns had a good point earlier on, that if all the points of isolation are in the same location then that is a different situation to them being scattered about an installation.
 

Reply to Two pairs of tails from meter to two DB's - what do I record in Section L? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
328
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
307
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
367

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
J
  • Article
SVP (grey water) gases leaking out - What do you see (pics)? Hi all, I would really appreciate your eyes on these pictures - What do you see ...
Replies
0
Views
183
Jayp07
J

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top