Evening all, been a long time since I posted on here but I could use some advice if there's any going!
I've been asked to provide an EICR for a small building we look after for our client under contract. We are all done physically on site, but I've hit a snag filling out the report itself, in particular with Section L - Particulars of Installation at the Origin.
There is a small cupboard with the supply cable / cut-out / meter. The tails travel from the meter into an insulated adaptable box, and two pairs of tails come out, each pair feeding it's own three-phase x 8-way D - 24 circuits per DB / 48 circuits for the whole building.
Each DB has an RCD as a Main Switch - historically the supply to DB2 was taken out of DB1 as a sub-main supply. However due to problems with the 100A RCD main switch for DB1 tripping almost daily due to overload, due to it carrying the load for both DB's, we decided to put DB2 on its own supply from the meter a year or two ago.
This solved the overload problem, but now I have a problem filling out the details of the Main Switch - under the new configuration, there is, I would suggest no Main Switch as such - at least, there is no longer a single switch that can isolate the whole building / installation.
So is it a case of writing N/A in the boxes because there is no main switch?
Also, does the lack of a main switch breach BS7671? Should it be coded in Section F and if so how should it be coded?
Any advice would be gratefully received...
Thanks
Ben
I've been asked to provide an EICR for a small building we look after for our client under contract. We are all done physically on site, but I've hit a snag filling out the report itself, in particular with Section L - Particulars of Installation at the Origin.
There is a small cupboard with the supply cable / cut-out / meter. The tails travel from the meter into an insulated adaptable box, and two pairs of tails come out, each pair feeding it's own three-phase x 8-way D - 24 circuits per DB / 48 circuits for the whole building.
Each DB has an RCD as a Main Switch - historically the supply to DB2 was taken out of DB1 as a sub-main supply. However due to problems with the 100A RCD main switch for DB1 tripping almost daily due to overload, due to it carrying the load for both DB's, we decided to put DB2 on its own supply from the meter a year or two ago.
This solved the overload problem, but now I have a problem filling out the details of the Main Switch - under the new configuration, there is, I would suggest no Main Switch as such - at least, there is no longer a single switch that can isolate the whole building / installation.
So is it a case of writing N/A in the boxes because there is no main switch?
Also, does the lack of a main switch breach BS7671? Should it be coded in Section F and if so how should it be coded?
Any advice would be gratefully received...
Thanks
Ben