Type A RCD upstream,downstream or up the swanny. | on ElectriciansForums
Discuss Type A RCD upstream,downstream or up the swanny. in the UK Electrical Forum area at ElectriciansForums.net
hertfordshire
Hi All.
I've got to get a job ready for Pod point to install a car charging unit.
They need the gas bonding to be done,which is quite straight forward.
And they need a type A RCD put in the board.
The point is going in a garage which has a sub board feed from a B40 mcb on the main house board,which has type AC RCDs.
Im finding it difficult to get hold of more specific information from them. But Im guessing they want the AC RCD covering the B40 mcb in the main board swapping out for a type A ?
Should the subboard also have a type A RCD?
I've only briefly visited the job,so I still have to get my bearings with it all.
Any thoughts from those that know more than me on this?
DC-sensitive type B RCDs are quite expensive, check if it is actually needed as some EV chargers only expect type A feeding them as they handle DC leaks themselves.
If the main board has a 30mA RCD feeding the garage then it does not need a local RCD. It won't do any harm, but it is not needed, and means there are two possible devices to reset if tripped.
If the garage feed is SWA then it does not need a RCD feeding it (unless TT so Ze too high) so it would be better to have the RCD at the garage CU and a non-RCD MCB on the supply. Less chance of a garage/EV fault taking out house electrics.
Brilliant thanks , they have stipulated a type A rcd .
Just to add, if you can change the board RCD to type A it is generally a good thing as better protects other circuits from electronic-style faults.
But see what you find on a closer inspection. You might also find problems in getting new parts for it if the main board is quite old which makes the best solution a more complicated judgment.
If in doubt get some photos, @westward10 is the one to ask for any unusual CU parts, he is a walking encyclopedia!
Thank you very much for taking the time. Much appreciated ?
If the Sub main is SWA remove from DB and fit in switch fuse sized to cable size etc and feed from Tails with Henry's
Garage end fit a new DB with Separte DP RCBO for each circuit Pod point will fit a CT to garage supply and set the clamp current to the size of the switch fuse or lower to stop any overloads of the sub main
Any questions PM me as quite knowledgeable on there use and installation
And a type A RCBO is fine if you have a AC downstream it will be Blinded by the DC and might not work so essential to get this right
Sorry, but can't get this image out of head now...
Like this?
[ElectriciansForums.net] Type A RCD upstream,downstream or up the swanny.
Fit an MCB in the garage board and route it through a separate type a rcd?
Typical Pod Point though... get all the hard work done as they cant and dont do it then come fit a charger...
I use the small enclosures with Type A RCD/RCBOs in from WCED you can buy one on amazon for ÂŁ25-30
Reply to Type A RCD upstream,downstream or up the swanny. in the UK Electrical Forum area at ElectriciansForums.net
Thanks Westward, and that last paragraph with the Note about no characteristic marking is exactly what I needed to see.
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...