Hi all. What are your thoughts on coding type AC RCDs when doing EICR's?
I understand the issue on DC currents preventing RCd's from functioning correctly.
The Am2 version of code breakers suggests a C2 coding for: "....type AC RCD and has pulsating DC currents from connected equipment such as EV,PV, switch mode power supplies, domestic appliances with VSDs etc..."

I get the first two, (EV,PV) they should be fairly obvious, how are we making judgement calls on the other items, esp if we are in an unoccupied house between tenants for example?
 
I would have hoped that the BPG#4 would have been updated by now for AM2 but nothing yet.

My own feeling is C2 would only be merited if the sockets are likely to be used outdoors and it has PV/EV, as that is when the possibility of DC blinding of the RCD is a real risk to life in the event of a damaged extension lead, inverter fault, etc. But for sockets in general it would have to be minimum C3 these days as practically everything has electronics in it.
 
Not according to codebreakers.....
Probably not. But don't they list no RCD as C2 always, whereas BPG#4 has C3 or C2 depending on the circumstances?

The problem is how do you deal with plugged-in equipment, as if you have to cover all possibilities we would have to fit the horrendously expensive type B in that case!
 
Why is this book the go to it doesn't deserve the ink and paper it uses in it's production
I think it's a useful tool to help you think through the inspection and prompt you as to things to look for and consider. My point was to get thoughts on the suggestion that pretty much all type AC rcds you come across are a C2, or how do we go about making a judgement as to whether there are likely to be pulsating dc currents present
 
I think it's a useful tool to help you think through the inspection and prompt you as to things to look for and consider. My point was to get thoughts on the suggestion that pretty much all type AC rcds you come across are a C2, or how do we go about making a judgement as to whether there are likely to be pulsating dc currents present
The problem is a one size fits all approach doesn't always work and the it must be right cos it says so in codebreakers does not absolve the person doing the EICR from making the correct decision, the most useful tool is actually BS7671 and not some book that carries the opinions of those who have not seen the exact scenario and circumstances you are working with. If you speak to people who contributed to codebreakers they don't necessarily agree with all the outcomes listed so it is clearly flawed
 

Reply to Type AC RCD's and EICR's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
You would think there is already one there, but the builder hasn't mentioned this. He's pretty savvy, and I believe he would have mentioned this...
    • Informative
Replies
4
Views
2K
  • Question
Protection from what? What kind of problem with the inverter is going to be helped by having an RCD on the circuit?
Replies
5
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top