Hi all, not been around in a while but I'm working through a quote at the moment and found this at the end of the equipment (AC kit) suppliers quote.
From the icons provided were definately talking B type and not B curve.
For the job in question this one paragraph statement could add upwards of ÂŁ10k to the electrical quote.
There are seven outdoor units and forty-four indoor, across 8 circuits.
The DB for the outdoor units will be a new, dedicated, install and could arguably be up front protected but this approach has it problems.
TP 40A type B RCCBs range from ÂŁ650-1200 each.
SP 32A type B RCDs don't exist in a single module (schneider Acti9) and would require major modifications.
I've not come across B type RCDs being specified for fire protection.
The research I've done makes no mention of fire protection provision by type B rcds.
Yes, these are inverted devices and may blind other type RCDs but there in no other regulatory requirement for an RCD other than this Manufacturer's Instruction.
What are peoples thoughts on this.
I am trying to talk to someone at the manufactures but they are a global mega Corp and getting hold of a person is nigh on impossible.
From the icons provided were definately talking B type and not B curve.
For the job in question this one paragraph statement could add upwards of ÂŁ10k to the electrical quote.
There are seven outdoor units and forty-four indoor, across 8 circuits.
The DB for the outdoor units will be a new, dedicated, install and could arguably be up front protected but this approach has it problems.
TP 40A type B RCCBs range from ÂŁ650-1200 each.
SP 32A type B RCDs don't exist in a single module (schneider Acti9) and would require major modifications.
I've not come across B type RCDs being specified for fire protection.
The research I've done makes no mention of fire protection provision by type B rcds.
Yes, these are inverted devices and may blind other type RCDs but there in no other regulatory requirement for an RCD other than this Manufacturer's Instruction.
What are peoples thoughts on this.
I am trying to talk to someone at the manufactures but they are a global mega Corp and getting hold of a person is nigh on impossible.