Simon Torr

hi all,

Domestic installation question

I have an Hager split board, left hand controlled by an RCD.
100 A Main switch
RCD 63a, with upstairs and downstairs sockets 32a, 1 x 16a sockets all type C, there is also 1 x type B 20a MTN 120 for sockets.

The type B has two T&E cables, both ending in the garage for sockets. One cable enters the board via the back of the board, and the other disappears behind the mounting plate for the meeter. I'm not to know why there are two cables, but they there.

The reason for my question. I'm installing garage lights and socket via 63a board 20a and 6a, SWA 2.5 twin and earth .5 meter from main board

The 17th edition states that the board and mainly sockets and lighting should be split (down stair sockets and upstairs lights on one side of the board, and the opposite on the other side of the board). Alas

My question is why all the type C MCB's, From my understand type C characteristics is time delay.
Shouldn't type B be the preferred MCB or am I missing the plot, as the house is the normal two up two down.

:59:
 
As long as the install complies with the Zs values it doesn't really matter as it will still meet tripping time requirements unless you have Zs issues wouldn't concern yourself with it, ....who knows why the previous 'Electrician?' fitted type C we can only ponder all day as domestically I see little advantage.
 
Why do you think there are C type CB's used?
Large start up loads?
Or whatever was in the back of the van?
Have you calculated, or measured the Zs of the circuits?
Do they comply?

If you are adding new circuits, maybe time to fit another RCD, or take the new circuit off a RCBO?
 
hi all,

Domestic installation question

I have an Hager split board, left hand controlled by an RCD.
100 A Main switch
RCD 63a, with upstairs and downstairs sockets 32a, 1 x 16a sockets all type C, there is also 1 x type B 20a MTN 120 for sockets.

The type B has two T&E cables, both ending in the garage for sockets. One cable enters the board via the back of the board, and the other disappears behind the mounting plate for the meeter. I'm not to know why there are two cables, but they there.

The reason for my question. I'm installing garage lights and socket via 63a board 20a and 6a, SWA 2.5 twin and earth .5 meter from main board

The 17th edition states that the board and mainly sockets and lighting should be split (down stair sockets and upstairs lights on one side of the board, and the opposite on the other side of the board). Alas

My question is why all the type C MCB's, From my understand type C characteristics is time delay.
Shouldn't type B be the preferred MCB or am I missing the plot, as the house is the normal two up two down.

:59:
Um no, however as Darkwood
 
hi all,

Domestic installation question

I have an Hager split board, left hand controlled by an RCD.
100 A Main switch
RCD 63a, with upstairs and downstairs sockets 32a, 1 x 16a sockets all type C, there is also 1 x type B 20a MTN 120 for sockets.

The type B has two T&E cables, both ending in the garage for sockets. One cable enters the board via the back of the board, and the other disappears behind the mounting plate for the meeter. I'm not to know why there are two cables, but they there.

The reason for my question. I'm installing garage lights and socket via 63a board 20a and 6a, SWA 2.5 twin and earth .5 meter from main board

The 17th edition states that the board and mainly sockets and lighting should be split (down stair sockets and upstairs lights on one side of the board, and the opposite on the other side of the board). Alas

My question is why all the type C MCB's, From my understand type C characteristics is time delay.
Shouldn't type B be the preferred MCB or am I missing the plot, as the house is the normal two up two down.

:59:

Missed that question... you are kind of there but not correct... its inrush allowance , however in a short circuit of little impedance the current will be so high that the type of the mcb is irrelevant.
 
Why do people panic if anything other than a type B is fitted? lol.
One good reason to fit type C's in a domestic situation is to prevent or at least reduce the risk of lamp failure on lighting circuits popping a type B,which is very common. In situations where less able or elderly people live much more attention should be paid to this,and yet you rarely see type C's fitted to lighting circuits
 

Reply to type c mcb on domestic hager board in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
634
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2
Replies
47
Views
4K
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K
  • Question
Single Pole, Single Pole Switched Neutral, and Double Pole are all different things. Hager RCBO's are Single Pole. I was recommending Single Pole...
Replies
33
Views
5K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks