Type of supply tncs or tt | on ElectriciansForums
Discuss Type of supply tncs or tt in the UK Electrical Forum area at ElectriciansForums.net
newfutile
Nearly Esteemed
Supporter
hemel hempstead
Ukpn have put a supply in for us to feed an outside cabinet, which will eventually supply foul water, sewage pump's.
They have supplied an earth but they have refused a meter until we supply a TT earth and a 30 ma rcd.
I have now done this and I measured 20 ohms between our earth and there's.
Has anyone come across anything like this before?
  • [ElectriciansForums.net] Type of supply tncs or tt
I think he did mention that it’s classed as temporary,even though it’s not really and once we have the pumps I will wire them to there own rcbo, I only fitted a socket for convenience and so UKPN can do a polarity test.
What's their Ze and your Ra
TN-S or TNC-S, I've no idea why they've provided an earth but say you cannot use it (if im understanding correctly), be interested to know why !
I think they'll only accept TT for what they class as temporary supplies but once the fixed installation is complete it's fine to connect to the DNO earth.
My guess is that they'll have provided a TNCS supply but as far as they're concerned it's still a building site, for which TNCS is prohibited, hence why you need a temporary TT with RCD in place.
Reply to Type of supply tncs or tt in the UK Electrical Forum area at ElectriciansForums.net
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...