Replacing 15 year old FAR Italian manifolds (2 downstairs, 1 up) with new Warmup units. However, old actuators have 4 core and new only have 2 core. Can someone please explain what the additional 2 cores are used for in the old actuators and how to modify the wiring for the new, and perhaps if at all possible supply a wiring diagram for an S Plan system with 4 zone valves - 1 for manifolds downstairs, 1 for manifold upstairs, 1 for two towel rails upstairs, 1 for hot water. Many thanks for any help.
 
4 wire actuators incorporate a switch that operates when the actuator is 'on'. This switch will be connected in parallel with the ones on the other actuators, and used to turn the boiler and pump on.
A 2 wire actuator system will have a diode connected to the 'live' wire of each actuator, the second wire from each of the diodes are all connected together and connected to a relay. The contacts of this relay are then used to switch on the pump and boiler.
 
4 wire actuators incorporate a switch that operates when the actuator is 'on'. This switch will be connected in parallel with the ones on the other actuators, and used to turn the boiler and pump on.
A 2 wire actuator system will have a diode connected to the 'live' wire of each actuator, the second wire from each of the diodes are all connected together and connected to a relay. The contacts of this relay are then used to switch on the pump and boiler.
Thank you, thats very helpful.
 
You get similar with 2 port zone valves. Some have just a blue and brown wire (plus sometimes an earth) which operates the valve motor. Some also have grey and orange wires, which connect to a microswitch which operates when the valve is open.
 

Reply to UFH - 4 core old and 2 core new Actuators in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

S
  • Article
UFH and zone valves help? Hi all Got an existing combi with 3rd party controls. There is a towel rail zone with 2 port valve and UFH manifold with...
Replies
0
Views
123
Scott_D
S
Unfortunately I don't think you will get an "off the shelf" diagram for the system you are trying to do The Wiser system is very adaptable but it...
Replies
1
Views
428

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top