Done CU change recently, customer had already brought a 'nice' crabtree starbreaker...! Never been keen on these.

Been having bit of prob.

All tested and no faults on installation itself.

All fine on first 3module RCD all circuits holding in, but on 2nd 2module rcd along... 3 circuits on this as soon as turn on any of these 3 MCB's bang goes the RCD. First RCD stays in, so no shared neutrals there. So tried each circuit on first RCD side all hold in fine ?

Have tried taking everthing out CU except incoming tails and neutral links, then put each of these 3 circuits in on there own, on the 2nd RCD side and each one trips the RCD ?

Replaced the RCD and still same prob ?

Am I missing something ?

Could the internal busbar be faulty somehow :confused:

Cheers Sy:eek:
 
I've accidentally mixed my neutrals up i.e. non-rcd neutrals to rcd neutral bar, rcd neutrals to non bar. rcd works by balancing line A and neutral A so should only operate if there is an imbalance. if a twin rcd board, temp swap rcd's to eliminate faulty rcd. Assuming fault still occurs, check circuit by circuit. If fault can't be isolated by circuit fault must be in DB.Please don't think this is an egg sucking class if you've already tried this !!
 
try putting the 3 suspect MCBs in the 1st RCD's bay temporarliy and see if they trip it.

You say youve removed everything but tails and neutral link... you have removed anything linking the two neutral bars when the two rcds are in use, havent you?
 

Reply to Umm strange...? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
162
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
830
Very technical :D
    • Like
Replies
9
Views
590

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top