C

chalky06

Hi all, as has frequently been pointed out the customer is always right!!!! The lighting is on the old twin (no earth) and according to customer I can just attach some new cable to this for his new lights he wants putting up in different locations. In my eyes morally and professionally wrong as he is refusing a re wire even after the points of safety and current have been pointed out!! am about to tell him to find some one else who is willing to do it. Any one have any more ammunition on this??
 
i assume that his new lights are classI, if so, then no way without a cpc. either a rewire or a sinle cpc from CU to each point 2.5mm if protected, 4.0mm if not. otherwise, tell the idiot to do one.
 
from the OP , i understand that the customer wants additional lights fitting, so even so, wiring to these must include a cpc, even if they are classII.

411.3.1.1.
 
If theres origionally a class1 light fitting in a circuit with no cpc, is a straight swap allowed if thats what the customer wants, even after being explained the issues?
 
not on my watch, it isn't. think about it. if you swap that fitting witout adding a cpc and earthing the metalwork, customer goes to change a lamp /bulb, gets a shock, who's up before the judge?????
 
Just makes me think how fittings could be like that for years having no earth in the first place.. Why would they have wired up bulidings like that from the start?
 
Considering the quality of light fittings nowadays, i would not even contemplate fitting a class 1 , not even in my own house. In the old days fittings were 2 wire pendants so nowhere for an earth anyway.
The customer is NOT always right but the customer is always the customer.
P&S 2010.
 

Reply to Un earthed lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
908
It applies to commercial if it shares the same supply as a dwelling.
Replies
4
Views
571

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top