Unable to access any(but can see most) of the round type screw terminal joint boxes.
Hello,
I carried out anEICR last week, and the entire house is filled with SELV recessed downlighting.
All of the (78fittings) have been skimmed around/over at some point, and the(dangeling) round type screw terminal joint boxes are two large topull down through the lamp aperture.
I have pointed thisout to the customer, and explained that unless he accepts materialdamage to the ceiling/s so that I can access the terminals, this willbe entered on the report as a limitation (inspection and testing).
Iwas able to get acceptable R1-R2 continuity at switch drops & extractor fans.
My dilemma is,... ifthis many joint boxes are inaccessible, I feel that even with thestated (and agreed) limitation it still warrants a code 2, (526.3 &14.5.2-5), and so resulting in an unsatisfactory outcome, (all of theother circuits/ancillaries are now ok), it just seems to be harsh,but ultimately I do not know, and can not tell, if these lightingcircuits are either good or bad.
What do others do inthis situation please?
Many thanks.
Hello,
I carried out anEICR last week, and the entire house is filled with SELV recessed downlighting.
All of the (78fittings) have been skimmed around/over at some point, and the(dangeling) round type screw terminal joint boxes are two large topull down through the lamp aperture.
I have pointed thisout to the customer, and explained that unless he accepts materialdamage to the ceiling/s so that I can access the terminals, this willbe entered on the report as a limitation (inspection and testing).
Iwas able to get acceptable R1-R2 continuity at switch drops & extractor fans.
My dilemma is,... ifthis many joint boxes are inaccessible, I feel that even with thestated (and agreed) limitation it still warrants a code 2, (526.3 &14.5.2-5), and so resulting in an unsatisfactory outcome, (all of theother circuits/ancillaries are now ok), it just seems to be harsh,but ultimately I do not know, and can not tell, if these lightingcircuits are either good or bad.
What do others do inthis situation please?
Many thanks.