Hi all, we are currently carrying out PIR's on resisdental properties/flats, but only the common areas,landlord supplies.My problem is that today i came across a landlords supply which share its supply with lots of flats and for various reasons i was unable to turn off supply, disconnect main earth and carry out Ze test. So my question is: for page three(main characteristics) do i just write lim down for Ze and PFC or maximum values? i.e for TNC-S 0.35ohms unsure of max PFC? kind regards simon
 
PFC can still be measured as the main bonds and earth are connected for this test. As for the Ze on a PIR that i could not isolate i would test with earth connected and note on cert that Zdb has been taken as Ze.
 
okay no problem will take the measurement from landlords db as i cant pull main fuse to test pfc as im aware the main bonding/earth should be left connected due to parallel paths/worst case.
 
PIR certs have a very useful limitations section on the front page.
As long as you can reasonably justify your limitations, i.e. 'unable to test for Ze as not safe to remove main earth', then just put LIM in relevant box.

I often find that when I carry out a PIR in an occupied unit/property you just cant go disconnecting supplies, or isolate server circuits, or remove sensitive equipment to enable an IR test. there's always something stopping you carrying out all the tests, so you just go for a LIM and justify it. just don't take the ****!
 
Last edited by a moderator:
okay no problem will take the measurement from landlords db as i cant pull main fuse to test pfc as im aware the main bonding/earth should be left connected due to parallel paths/worst case.

Yes, I'd prefer to see a value in the Ze box and an explanation that the value was measured with all bonding etc. in place due to resident constraints.

Why would you 'pull the main fuse' to do PFC?
 

Reply to unable to measure Ze! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Sticky
Hi Richard, thanks for your comment. The relay is rated 12A peak. It's also worth noting that a relay contact will perform differently depending...
    • Like
    • Winner
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top