C

chloebear

:confused: Just wanted to know the position regarding cert filling (NicEic) when faced with the situation that prvents you from takeing a Ze reading - i.e. multi site office fed with 3 phase pme supply & therefore unable to disconnect the main incomming earth to conduct the test.
 
Call the supplier and enquire what it should be and fill this value in. I'd also then measure as close to supply as possible to have a reference against Zs values
 
Is this a PIR ? if it is then you will have to mark it down as a limitation. Still try and take it and put it on the cert.

If there are old certificates about then even taking the Ze with the earth conductor connected, as long as it's not higher than the original you have a good idea that all is well.

If you have done an install and it is an EIC then if the install is on a sub board then you can take the Zdb as your Ze on the certificate. If there is just the one DB then I'm afraid you will have to mark it down under deviations from the BS 7671-2008 on your schedule of results
 
Call the supplier and enquire what it should be and fill this value in. I'd also then measure as close to supply as possible to have a reference against Zs values

There's your answer, it's all very well sticking down 0.35, 0.80 or whatever your supplier quotes from ESQCR 2002 but you're better off with a measurement as close to the origin as possible with parallel paths still connected, adding a note to the report/certificate as Malcolm says.
 

Reply to Unable to take Ze Reading in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Your tester is obviously picking up something that's stopping it carry out the test. If you've checked the leads & the tester settings and all is...
Replies
22
Views
3K
  • Question
Thanks for the replies, unfortunately I can't check the site earthing, I would expect the site to be a TT private distribution system. I've...
Replies
4
Views
6K
Hi Newthy, any chance I could get those sheets emailed to me, trying to open the links on here but it keeps running into an error and wont load...
Replies
36
Views
9K
  • Question
This looks like a decent project to get your teeth into. It may be worth your while looking through the directory on here for your area as your...
Replies
8
Views
2K
  • Question
Yes, certainly my view on the matter as well! The TN-C-S option would not be so bad if it were a ring circuit (so no single PEN break causing...
2
Replies
29
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks