G

Gossy

The underfloor heating controller says it will be able to pull a maximum of 16 Amps.

The supply is from a 20 RCBO. 2.5mm Twin and earth to a 13 Amp switched fused spur. The load side of the spur feeds the underfloor heating controller.

The owner is saying that if for what ever reason the underfloor heating controller was pulling 18 Amps, the fuse spur will not blow. I know this is the case as 13 Amp fuse will take around 19 Amps for a long period of time. The undefloor heating has been designed to take 8 Amps but from an electrical point of view is this circuit unsafe in anyway?

Help would be appreciated
 
1. what's the kw rating of the mat?

2. how has the customer arrived at this figure of 18A?

3. have you done any testing?

answer the above and you may get some help.
 
The underfloor heating controller says it will be able to pull a maximum of 16 Amps.

The supply is from a 20 RCBO. 2.5mm Twin and earth to a 13 Amp switched fused spur. The load side of the spur feeds the underfloor heating controller.

The owner is saying that if for what ever reason the underfloor heating controller was pulling 18 Amps, the fuse spur will not blow. I know this is the case as 13 Amp fuse will take around 19 Amps for a long period of time. The undefloor heating has been designed to take 8 Amps but from an electrical point of view is this circuit unsafe in anyway?

Help would be appreciated

The controller does not pull 16 amps , it has a maximum rating of 16 amps .

You say the total load of the mat is 8 amps so what is the problem ?
 

Reply to Underfloor heating Controller in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

I think that's the point I was trying to illustrate. If volt free contacts on a device on one supply are switching mains voltage coming from...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top