The UFH cable has an earthed screen and damage will cause an earth fault which will trip an RCD.
Only way is an insulation test @500v to establish whether the cable is sound.
 
Mate just tested it. Reckons neutral has been shorted to the earth.

What does he do on the insulation test?

a screw through a 3mm cable... madness!
 
Have you had the whole bathroom area fitted with under floor heating.
If you have, did you inform your bath room fitter of the same.
 
Mate just tested it. Reckons neutral has been shorted to the earth.

What does he do on the insulation test?

a screw through a 3mm cable... madness!

A multimeter wont be much use,you need a 500v insulation tester,and test between the live core and the earthed screen of the cable..you should expect a reading of hundreds of megohms if the cable is sound...<1 megohm would be a worry....if damaged you may get a dead short,ie 0.00 megohms. If the IR is OK test the continuity of the cable using your multimeter....the reading will be in ohms and should match the manufacturers declared resistance for the legnth/rating cable you have.
 
Last edited by a moderator:
I'm guessing the insulation test wont be much use now.... especially if the neutral is shorted to the earth.

Does that simply point to a screw through the cable?
 
Did your mate test the cable completely disconnected??....if not you will get a N-E reading if the N is still connected.
If you are using a multimeter to find a fault you are likely to get misled....a high voltage insulation resistance test is still essential before ripping it all up...there's no way I would be relying on a multimeter.
 
Last edited by a moderator:
I'm guessing the insulation test wont be much use now.... especially if the neutral is shorted to the earth.

Does that simply point to a screw through the cable?
If the screw (metal) is providing a fault path between both conductors then...yes
 
Last edited by a moderator:

Reply to Underfloor Heating Drilled Through!?! in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
694
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

im just assuming that they are designed to be surrounded by material, and would heat to a certain amount, spreading the heat into the material...
Replies
4
Views
306
  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top