madger

-
Joined
Dec 14, 2011
Messages
7
Reaction score
0
Hi there, I’m looking for some advice regarding underfloor heating. The conservatory is 20.9m2 and total power is 3.344kw. At 230v this gives me a current rating of 14.54A. The controller is rated at 16A, normally I supply controller via 13A switched fused spur but with this increased loading I believe I can supply via a relay? Could anyone please advise what type of relay I would require? and if possible where it can be purchased. It would need to fit locally into a dry lining box. Many thanks in advance.
 
A contactor would be preferred,with a 16/20a feed to the contacts as a radial from the CU via a 20a isolator, and your controller feeding the coil. There are likely to be several elements on such a load and these could be split over the 3 poles of the contactor.
There is no way you will fit a contactor..(or relay)...in a dry lining box.
 
The trouble with the contactor option is that it has to be mounted locally, thus every time the heating goes on/off you get a great 'clunk' I'm sure i saw a power relay on a system a couple of years back mounted in a double 48mm dry liner?

Should also have added that dedicated supply was no go due to construction of house/position of fuse board so local ring utilised.
 
Can you clamp the circuit to see what it is actually pulling, it may well be taking a little bit less than you have calculated, especially if your voltage is higher than 230. You may find the current a little less than 13A. worth a look before you start trying to fit a contactor in.
 
Will try that Roger, wanted to cover my bases so have done little research and found 16a in-line fuse holder which I can use in conjunction with 20A dp switch instead of 13a fused spur if load is greater than 13a as controller rated at 16a. With regards to the power relay (for future reference with increased loads) I would still appreciate any help available.
 
The trouble with the contactor option is that it has to be mounted locally, thus every time the heating goes on/off you get a great 'clunk' I'm sure i saw a power relay on a system a couple of years back mounted in a double 48mm dry liner?

Should also have added that dedicated supply was no go due to construction of house/position of fuse board so local ring utilised.

When you find one let us know, I've had to do the same in the past and it looks crap in a conservatory and the clunk noise int very good either
 
Sorry to confuse, my controller is rated at 16A so no problem. A Contactor could be used to switch load up to say 20A on a 32A mcb as the controller is only rated at 16A so in this type of situation the controller would operate the contactor. It was in this sort of scenario that I was wondering if an alternative to a contactor was available.
 
That's what i plan to do if it pulls more than 13A, won't know for sure untill put clamp meter on when i connect up. Also need to check with manufacturer before fitting mat as calculations done using 160wm2 mats when i may be able to get away with 130wm2 as Amtico flooring being fitted over Ecomax duo top boards.
 
I think this is one of those cases of prior planning...
Was the floor installed without consulting you, or is it not down yet? If it was installed without adequate supply being available then that is poor design.
 

Reply to Underfloor Heating over 13A?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K
I think that's the point I was trying to illustrate. If volt free contacts on a device on one supply are switching mains voltage coming from...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top