Hi,

Now I understand that this question may seem pointless, so humour me anyway...

A lady had underfloor heating installed about 10 months ago along with her new kitchen...

I was there for the kitchen install but didn't do the mats, there are two mats serving her kitchen and utility room, both are connected to the same programmer....

after she had issues with 'overloading', as she was 'reliably' informed, the mats were disconnected...

anyway ive had a look and it is in fact a L-E fault on just one mat... so connected one back in and its all good with a reading of >999 from L+N-E

the other mat has a reading of 0.01 megohms and 17,000ohm for continuity from L+N-E....

she was sold a new programmer by the company as i passed this info on to the person who has taken responsibility for the install, and they called the technical support - who told him the readings are normal and that a new programmer at ÂŁ80 was required....

Anyway this mat trips the RCD obviously, but with a continuity of 17k if it was connected to just an MCB it would have a fault current of 13mA? and therefore the mat would work again?
 
yep fair enough, have called technical support and they will send a new replacement mat, but that cost is substantially outweighed by the labor cost of lifting and replacing all her nice expensive floor tiles... hey ho not my kitchen though!
 
na, nice thought though.. the 2 mats hit a jb before entering the programmer, i isolated the mat at the jb, so not the probe.... i agree with the tech bloke tho, its weird it worked fine for 6 months then one day POOF
 
They do - it doesnt take much to nik the cable then with the heating and cooling it just gives up. Plus some cable mats have very little insulation to protect them.
 

Reply to Underfloor Heating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
943

Similar threads

The instructions tell you to test the insulation and you already know from the result of the previous test that the L and N are not insulated from...
Replies
4
Views
528
davesparks
D
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top