70mm 2 core SWA has a CSA of armouring of 84mm2 ,with 70mm 2core the required CSA of the armouring would be 79mm2 so using 70mm two core SWA will be fine.

Only as the cables CPC, If any main bonding is involved then it will not comply!! BTW the CSA of armouring on a 2 core XLPE swa cable (which is now what you would receive from the wholesalers unless you specify PVC insulated) is 80mm...

With the sort of distances were talking about here, i'd still be calculating if that SW armouring is of a suitable size, even as a CPC!!
 
Hi Darkwood
We have calculated the load to be approx 5Kw and its actually a service building, so it will have some building services which will need to be earthed.
As I understand it if we cannot obtain the desired Zs value from the DNO, then we would install a separate earth and treat the service building as a TT system.
Is that not how you see it?. I look forward to hearing from you
Skyline2500cc
 
Can you show your VD calcs please and is lighting load included - at that distance you may be pushing it with 5KW ? I did a quick rough calc and get nearer 3kw hence my comment on the kettle.
For us to comment we need to know how your arriving at these figures.

Your use of the word Approx also means I would be figuring room for expansion within reason

What is the measured Ze at origin and what calculated Zs do you get + what is the nature of the OCPD and its type.... rather than using terms like 'if we cannot meet Zs' why not estimate it once you have selected your cable of choice.
 
Last edited by a moderator:
OK, maybe a dumb question but wouldn't it possibly be cheaper to get Hydro to put in a separate/new supply into this building (subject to the overhead cables, transformers etc)?
 
have you checked how much if you dig the trench and supply the cable etc.

yeah its expensive in inverness they must have spent a fortune when they upgraded all those overhead lines.

i drove past it last year and they dwarfed the old ones (are they 133kv or higher im not what exactly, we dont touch distribution)
 
my great aunt owns a chalet up in avimore a short drive from inverness so i can understand when you say its very expensive.

just so we are on the same page, how much were you quoted for say a 60a supply?
 
one of my clients needed a 3 phase supply. 400 yards from nearest pole. he dug the trench himself. still cost him 15K.
 
We already have the supply and it was installed by others with cost unknown. We install new LV plant and historically it can cost thousands to get a supply from an existing transformer to a new location.
I was once quoted ÂŁ600 to remove the meter and cutout so that we could replace the backboard with new because it was wood and had rotted away.
It took the guy two hrs tops from leaving his premises to returning.
 
have you checked how much if you dig the trench and supply the cable etc.

yeah its expensive in inverness they must have spent a fortune when they upgraded all those overhead lines.

i drove past it last year and they dwarfed the old ones (are they 133kv or higher im not what exactly, we dont touch distribution)

Do you mean these Muther FÂŁ$%ers?
Benvironment ? Scotland, meet your giant new pylons

So they can flog us all their Green power.
 
al i can say to these whingers is " bin your washing machine/tumble dryer/range cooker. do the washing on a stone by the river and cook over an open fire in the back yard".
 

Reply to Underground SWA Cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
895
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top