Engineer54
70mm 2 core SWA has a CSA of armouring of 84mm2 ,with 70mm 2core the required CSA of the armouring would be 79mm2 so using 70mm two core SWA will be fine.
Only as the cables CPC, If any main bonding is involved then it will not comply!! BTW the CSA of armouring on a 2 core XLPE swa cable (which is now what you would receive from the wholesalers unless you specify PVC insulated) is 80mm...
With the sort of distances were talking about here, i'd still be calculating if that SW armouring is of a suitable size, even as a CPC!!