could someone please help me with these knowledge question answers if finished nvq site diaries just got to answer these now..regards unit 307

The main types, their advantages and limitations of different electrical connections




use of correct testing methods, and





The implications on the choice of connections with regard to permanent or temporary purposes




[ElectriciansForums.net] underpinning knowledge nvq3

The requirements of joints and connections to be of strength and conductance to allow for the passage of fault currents and to prevent corrosion






The importance of using personal protective equipment and safe appropriate tools for specific jobs





IEE wiring regulations as specified in the latest British Standard for Electrical Installations relevant to types and uses of wiring systems, wiring enclosures and equipment







Where to find out about the principles of electrical theory which allow for the safe connection of electrical wiring systems and equipment
 
[FONT=&quot]1. [/FONT][FONT=&quot]What are the main types, their advantages and limitations of different electrical connections?[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]All terminations must be of the appropriate size and shape for the conductors terminating to them.[/FONT]
[FONT=&quot]Pillar terminals are most common. The conductor should fill the terminal. Over tightening can damage the thread, split the screw head and damage the conductor. Nut and washer type requires the cables to be formed around the thread and secured between an eye and washer. The conductor must not be too large for the eye. [/FONT]
[FONT=&quot]Shaping the conductor in the wrong direction (i.e. Anti clockwise), will tend to undo the conductor from the termination.[/FONT]
[FONT=&quot]Connectors similar to the pillar terminal method and often an additional clamp arrangement inside the connector.[/FONT]
[FONT=&quot]Crimps are compressed terminations. The correct size of crimp and clamping arrangement must be used for a secure connection.[/FONT]
[FONT=&quot]All of the above require appropriate insulation and identification. All terminations should be firmly made on the conductor. This will prevent high resistance joints that could lead to overheating and fire. There should not be any exposed conductor from the termination.[/FONT]

[FONT=&quot]2. [/FONT][FONT=&quot]What are the implications on the choice of connections with regard to permanent or temporary purposes?[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]Any electrical termination must be mechanically strong and electrically sound and fit for purpose. Any screwed connection must be accessible. Only solid connections e.g. soldered, crimped, brazed, even welded, none of which need not be accessible.[/FONT]
[FONT=&quot]All must have appropriate and adequate insulation to prevent ‘direct’ contact.(basic protection)[/FONT]
[FONT=&quot]This applies to both temporary and permanent connections.[/FONT]
[FONT=&quot]EAWR – Taped joints are not permitted.[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]3. [/FONT][FONT=&quot]What are the requirements of joints and connections to be of strength and conductance to allow for the passage of fault currents and to prevent corrosion?[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]Any joint or connection should not introduce any more resistance than that of the conductor itself. All terminations should be appropriate to the environment (e.g. high ambient temperatures). Where aluminium conductors are used appropriate terminations are needed to prevent corrosion.[/FONT]
[FONT=&quot]All conductors and terminations should be designed and selected to be suitable for handling fault currents for the duration of the fault in compliance with BS7671.[/FONT]

[FONT=&quot]4. [/FONT][FONT=&quot]What is the importance of using personal protective equipment and safe appropriate tools for specific jobs?[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]The use of PPE is a legal requirement under the HASAWA. Also the ‘Personal Protective Equipment at Work’ regulations 1992. Risk assessments determine the type of PPE required in a particular situation. Remember that PPE is the last line of defence from hazards (injury).[/FONT]
[FONT=&quot]The safe and appropriate use of tools involves training in their proper use.[/FONT]
[FONT=&quot]Using the correct tool for the task![/FONT]
[FONT=&quot]Keeping tools well maintained, i.e. Sharpe; handles securely fitted; insulation on hand tools not compromised.[/FONT]
[FONT=&quot]Other equipment must comply with the EAWR.[/FONT]

[FONT=&quot]5. [/FONT][FONT=&quot]What part of the IEE wiring regulations as specified in the latest British Standard for Electrical Installations are relevant to types and uses of wiring systems, wiring enclosures and equipment?[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]BS7671 – to install electrical installations in a safe manner as detailed in the wiring regulations and associated guidance notes.[/FONT]
[FONT=&quot]These documents set out the standard for installations and with the guidance notes how that standard is achieved.[/FONT]
[FONT=&quot]No part of the regulations is exempted from these requirements. There are however other authorities and bodies that can impose higher requirements (part one of the regs.)[/FONT]

[FONT=&quot]6. [/FONT][FONT=&quot]Where would you find out about the principles of electrical theory, which allow for the safe installation of electrical wiring systems, wiring enclosures and equipment?[/FONT]
[FONT=&quot] [/FONT]
[FONT=&quot]This should be done in line with the training and development of skills under supervision. Following manufacturers instructions and data sheets. In addition there are many practical textbooks that provide good guidance on installation techniques. This is normally provided through relevant training courses (e.g. C&G 2330).[/FONT]
 
[FONT=&amp]1. [/FONT][FONT=&amp]What are the main types, their advantages and limitations of different electrical connections?[/FONT]

[FONT=&amp]All terminations must be of the appropriate size and shape for the conductors terminating to them.[/FONT]
[FONT=&amp]Pillar terminals are most common. The conductor should fill the terminal. Over tightening can damage the thread, split the screw head and damage the conductor. Nut and washer type requires the cables to be formed around the thread and secured between an eye and washer. The conductor must not be too large for the eye. [/FONT]
[FONT=&amp]Shaping the conductor in the wrong direction (i.e. Anti clockwise), will tend to undo the conductor from the termination.[/FONT]
[FONT=&amp]Connectors similar to the pillar terminal method and often an additional clamp arrangement inside the connector.[/FONT]
[FONT=&amp]Crimps are compressed terminations. The correct size of crimp and clamping arrangement must be used for a secure connection.[/FONT]
[FONT=&amp]All of the above require appropriate insulation and identification. All terminations should be firmly made on the conductor. This will prevent high resistance joints that could lead to overheating and fire. There should not be any exposed conductor from the termination.[/FONT]

[FONT=&amp]2. [/FONT][FONT=&amp]What are the implications on the choice of connections with regard to permanent or temporary purposes?[/FONT]

[FONT=&amp]Any electrical termination must be mechanically strong and electrically sound and fit for purpose. Any screwed connection must be accessible. Only solid connections e.g. soldered, crimped, brazed, even welded, none of which need not be accessible.[/FONT]
[FONT=&amp]All must have appropriate and adequate insulation to prevent ‘direct’ contact.(basic protection)[/FONT]
[FONT=&amp]This applies to both temporary and permanent connections.[/FONT]
[FONT=&amp]EAWR – Taped joints are not permitted.[/FONT]

[FONT=&amp]3. [/FONT][FONT=&amp]What are the requirements of joints and connections to be of strength and conductance to allow for the passage of fault currents and to prevent corrosion?[/FONT]

[FONT=&amp]Any joint or connection should not introduce any more resistance than that of the conductor itself. All terminations should be appropriate to the environment (e.g. high ambient temperatures). Where aluminium conductors are used appropriate terminations are needed to prevent corrosion.[/FONT]
[FONT=&amp]All conductors and terminations should be designed and selected to be suitable for handling fault currents for the duration of the fault in compliance with BS7671.[/FONT]

[FONT=&amp]4. [/FONT][FONT=&amp]What is the importance of using personal protective equipment and safe appropriate tools for specific jobs?[/FONT]

[FONT=&amp]The use of PPE is a legal requirement under the HASAWA. Also the ‘Personal Protective Equipment at Work’ regulations 1992. Risk assessments determine the type of PPE required in a particular situation. Remember that PPE is the last line of defence from hazards (injury).[/FONT]
[FONT=&amp]The safe and appropriate use of tools involves training in their proper use.[/FONT]
[FONT=&amp]Using the correct tool for the task![/FONT]
[FONT=&amp]Keeping tools well maintained, i.e. Sharpe; handles securely fitted; insulation on hand tools not compromised.[/FONT]
[FONT=&amp]Other equipment must comply with the EAWR.[/FONT]

[FONT=&amp]5. [/FONT][FONT=&amp]What part of the IEE wiring regulations as specified in the latest British Standard for Electrical Installations are relevant to types and uses of wiring systems, wiring enclosures and equipment?[/FONT]

[FONT=&amp]BS7671 – to install electrical installations in a safe manner as detailed in the wiring regulations and associated guidance notes.[/FONT]
[FONT=&amp]These documents set out the standard for installations and with the guidance notes how that standard is achieved.[/FONT]
[FONT=&amp]No part of the regulations is exempted from these requirements. There are however other authorities and bodies that can impose higher requirements (part one of the regs.)[/FONT]

[FONT=&amp]6. [/FONT][FONT=&amp]Where would you find out about the principles of electrical theory, which allow for the safe installation of electrical wiring systems, wiring enclosures and equipment?[/FONT]

[FONT=&amp]This should be done in line with the training and development of skills under supervision. Following manufacturers instructions and data sheets. In addition there are many practical textbooks that provide good guidance on installation techniques. This is normally provided through relevant training courses (e.g. C&G 2330).[/FONT]

I can't believe you did that for him. Either very lazy or just incompetent
 
thank you mate just very badly worded questions i think but your answers are very well explained now and i totally understand them. and to you super spark stuart im sure you had to ask someone questions when you were doing your nvq in college or did you just get born with all the knowledge...YOU FOOL!thanks again for helping me macca much appriciated
 
I completed my NVQ with no help what so ever, my assessor came out twice throughout my whole level 3, ITS EASY!! Just requires dedication!

Evo55555, you need to grow up you child. With just two posts within the forum: one of them asking for answers of 7 questions and the other throwing insults. be gone young man
 

Reply to underpinning knowledge nvq3 in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
526
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top