ringer
-
Believe that I am (mostly) up to speed with electricity as applied to appliances (n.b. just realised as I wrote this, that is where the word appliances comes from, never occurred to me before!), so I am now trying to understand installation voltages. My aim is to learn/train eventually to become domestic installer, maybe more. Anyway, the point of this post is...
So I have my Fluke 6500 appliance tester plugged in and the home/idle screen shows the voltage/frequency of the supply as measured by the instrument. Current readings are:
VLN = 248.6v
VNE = 0.3v
49.9Hz
VLN is varying over time (over the last two minutes) from 247.7v up to 249.3v though I have seen it as high as 250.4 and as low as 239.8
VNE varies from 0.0 to 0.3, though does not constantly change like VLN does, just slowly.
When I switch on a toaster or microwave on the same circuit VNE jumps to 0.4v and VLN drops (sometimes) by up to 2v
When I switch on the kettle on the same circuit VNE jumps to 0.8v
Plugging the Fluke into another circuit, VNE remains constant (albeit non-zero) whether the kettle/toaster/microwave are on or not.
I can (sort of) understand that incoming voltage may vary. My main query/concern is about Vne
So my question (finally) is - are these readings 'normal', or does this indicate some sort of fault with my installation (or perhaps with the Fluke)?
So I have my Fluke 6500 appliance tester plugged in and the home/idle screen shows the voltage/frequency of the supply as measured by the instrument. Current readings are:
VLN = 248.6v
VNE = 0.3v
49.9Hz
VLN is varying over time (over the last two minutes) from 247.7v up to 249.3v though I have seen it as high as 250.4 and as low as 239.8
VNE varies from 0.0 to 0.3, though does not constantly change like VLN does, just slowly.
When I switch on a toaster or microwave on the same circuit VNE jumps to 0.4v and VLN drops (sometimes) by up to 2v
When I switch on the kettle on the same circuit VNE jumps to 0.8v
Plugging the Fluke into another circuit, VNE remains constant (albeit non-zero) whether the kettle/toaster/microwave are on or not.
I can (sort of) understand that incoming voltage may vary. My main query/concern is about Vne
So my question (finally) is - are these readings 'normal', or does this indicate some sort of fault with my installation (or perhaps with the Fluke)?