Believe that I am (mostly) up to speed with electricity as applied to appliances (n.b. just realised as I wrote this, that is where the word appliances comes from, never occurred to me before!), so I am now trying to understand installation voltages. My aim is to learn/train eventually to become domestic installer, maybe more. Anyway, the point of this post is...

So I have my Fluke 6500 appliance tester plugged in and the home/idle screen shows the voltage/frequency of the supply as measured by the instrument. Current readings are:
VLN = 248.6v
VNE = 0.3v
49.9Hz

VLN is varying over time (over the last two minutes) from 247.7v up to 249.3v though I have seen it as high as 250.4 and as low as 239.8
VNE varies from 0.0 to 0.3, though does not constantly change like VLN does, just slowly.
When I switch on a toaster or microwave on the same circuit VNE jumps to 0.4v and VLN drops (sometimes) by up to 2v
When I switch on the kettle on the same circuit VNE jumps to 0.8v
Plugging the Fluke into another circuit, VNE remains constant (albeit non-zero) whether the kettle/toaster/microwave are on or not.

I can (sort of) understand that incoming voltage may vary. My main query/concern is about Vne

So my question (finally) is - are these readings 'normal', or does this indicate some sort of fault with my installation (or perhaps with the Fluke)?
 
Believe that I am (mostly) up to speed with electricity as applied to appliances (n.b. just realised as I wrote this, that is where the word appliances comes from, never occurred to me before!), so I am now trying to understand installation voltages. My aim is to learn/train eventually to become domestic installer, maybe more. Anyway, the point of this post is...

So I have my Fluke 6500 appliance tester plugged in and the home/idle screen shows the voltage/frequency of the supply as measured by the instrument. Current readings are:
VLN = 248.6v
VNE = 0.3v
49.9Hz

VLN is varying over time (over the last two minutes) from 247.7v up to 249.3v though I have seen it as high as 250.4 and as low as 239.8
VNE varies from 0.0 to 0.3, though does not constantly change like VLN does, just slowly.
When I switch on a toaster or microwave on the same circuit VNE jumps to 0.4v and VLN drops (sometimes) by up to 2v
When I switch on the kettle on the same circuit VNE jumps to 0.8v
Plugging the Fluke into another circuit, VNE remains constant (albeit non-zero) whether the kettle/toaster/microwave are on or not.

I can (sort of) understand that incoming voltage may vary. My main query/concern is about Vne

So my question (finally) is - are these readings 'normal', or does this indicate some sort of fault with my installation (or perhaps with the Fluke)?

Voltage drop is dependant on current in that circuit only. measuring the voltage on another circuit will not show the drop, just the input voltage to the board.

Read up on ohms law.

THe NE you are measuring is the voltage drop on the neutral ONLY
 
Last edited:
leaking current mate, giving rise to a voltage

My college work from donkeys years ago just popped back into my head... I may be wrong but..

The current in the neutral will give rise to a voltage with respect to earth due to the resistance of the neutral cable. As the neutral and cpc are connected at the transformer and there is only current in the neutral there will be a voltage developed between the two. The measured voltage will be dependant on the resistance of the neutral and the current through it.Or has my head remembered it wrong???
 

Reply to Understanding installation voltages, particularly Vne in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top