Hi, newbie here. This is a bit of a hair splitting question. Doing PIR and lighting circuit has no earth.

The Electrical Safety Council's best practice guide on domestic CU replacements where the lighting circuit has no earth gives rise to a potential outcome (if the customer refuses to fund lighting circuit upgrade to be earthed) of risk assessment, RCD being fitted and warning notices applied etc.

If during my PIR I establish the lighting circuit is already on an RCD, should I be recording the 5xIdn operating time value for a belt and braces job, or should I not record the 5x test result and consider it a next stage activity after discussions with the customer.

I guess this is all about a small conflict between my approach of doing a wholesome job and the opportunity to charge for more time.

Many thanks in advance
SW
 
As it's on an RCD protected circuit, you should test it as such and record your results accordingly. You should then point out the reason for the failure, with two possible corrective actions. Either remove the circuit from the RCD (as there's little, but not no, point it being there without a CPC) or provide a CPC for it.

I say little point as it's still possible for current to find a route out of that circuit via other means and still trip the RCD.
 
You should still record it. It could be an internal fault with the device that means it won't trip at 1x but will at 5x (hence the 6 tests).
 
Hi, newbie here. This is a bit of a hair splitting question. Doing PIR and lighting circuit has no earth.

The Electrical Safety Council's best practice guide on domestic CU replacements where the lighting circuit has no earth gives rise to a potential outcome (if the customer refuses to fund lighting circuit upgrade to be earthed) of risk assessment, RCD being fitted and warning notices applied etc.

If during my PIR I establish the lighting circuit is already on an RCD, should I be recording the 5xIdn operating time value for a belt and braces job, or should I not record the 5x test result and consider it a next stage activity after discussions with the customer.

I guess this is all about a small conflict between my approach of doing a wholesome job and the opportunity to charge for more time.

Many thanks in advance
SW

What are your reasons for the question?

I can't see why you wouldn't carry out the 5X I Delta n test if you're standing there doing the other tests?

If any RCD/RCBO is used to provide additional protection then it must be rated at 30mA or less and be tested at 0.5, 1 and 5 X I Delta n on both halves of the wave cycle.
 

Reply to Unearthed Lighting Circuit & Need for 5x RCD Test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top