N
not_shocked_yet
Hi Everyone,
Please read ALL of the post below before contributing as the fault is unusual (for me, newly qualified).
My client called me out because turning on the lights in her (2009) converted stable block tripped the RCD (this is the main switch in the stable DB). Trying to re-set the rcd three times or so (it kept tripping) would then trip the (old) single RCD in the main house. To be clear, the house RCD is between the meter and the CCU.
Turning on the CB's in the stable block one at a time determined that one of the lighting circuits was causing the trip.
Anyway, whilst performing safe isolation in the stable (with a Kewtech KT64DL) with the supply turned off at the main CCU in the house I recorded a <25v across Line and Neutral but 65V across Earth and Line and Earth and Neutral.
Removing the L, N and E at the CB in the main house for the supply to the stable DB recorded a normal reading of <25V across all L.N and E combinations.
To be clear the DB at the stable is approximately 250 feet from the main CCU. I don't know yet what the cable is to the building (thinking it should be armoured) if it is joined somewhere en-route (which I doubt) otherwise it looks like 6mm or similar twin and 2.5mm earth (it's the red and black variety) - thats what is showing at the CCU and the DB anyway.
Testing voltage at the main switch at the CCU: With the main switch on I recorded 245v across L and N supply and <25V across E and N and E and L. HOWEVER with the main switch off I recorded <25V between L and N and 165V across E and N and E and L.
This is a TT system.
I used a 2 pole voltage tester to also test between E and L,N but still had a reading of over 50V.
Am I looking at a ghost voltage causing the readings? Is the house safe - it seems to be when the system is energised? Could there be a potential difference between bonding and supplementary bonding if the power went off?
The house is thatched and had a periodic inspection 6 months ago (not the stable however) for insurance purposes. No problems were reported at the time to the owner.
I ran an earth fault loop impedance test at CCU and recorded 30.5 ohms.
Hoping this is just a ghost voltage, any thoughts are most welcome.
Many thanks in advance!
I'm slightly confused but isn't the clients issue the lights tripping the rcd? If so you should be carrying out insulation tests on the circuits which are coupled to the rcd that is tripping. That would be my first step, not voltage tests. Id probably do an rcd test and a ramp test if I was you just to confirm the rcd is operating correctly too.
So you have 2 RCDs in series on this install?
Is one time delayed?
What testing have you carried out?
I read these fault finding threads and notice we get all these weird assumed voltages figures,voltages between this -that- Uncle Tom cobbly and his sister, I then have not the faintest idea of what they are on about
Where has all this obsession with voltage figures come from?
its important you neutralise, ie. link the supply neutral to your main earth terminal at the house,using 10mm earth wire, 30.5 ohms is far too high for loop impedance, should be about 0.2 ohms for your external loop impedance. tt ststems use the ground to carry fault current back to the supply traffo, if the ground impedance is not low enough your loop ie. line and earth will be too high.therefore it is common to use the supply neutral as a return conductor. going back to your fault, assuming your not importing any stray voltages from somewhere else. check supply cable to stable using your megger at 500v between each conductor and the ground outside[ stick one of the probes in the ground and the other probe on the conductors] and see if the cable in the ground has a leak, if it has there is a possibility of induction from another source. finally your cable to the stables should be supplied on the same side as the primary connection [fused correctly] of the houde rcd, if you are using a seperate rcd as a main isolaterin the stables. rcds in series dont operate correctly.
my gosh I have never read so much rubbish in my life.
I think you may have misunderstood neutralising a bit there.
As far as I know Neutralising is the term used in Ireland to describe the requirement to install an earth electrode connected to the MET of all PME fed installations.
Ay, but this isn't a PME system, so he's suggesting that the OP creates his own TNC, ...Not a very clever thing to do that!! ...
That's what I meant by him having misunderstood it, possibly I didn't make myself clear enough
In the south of Ireland:
The main protective conductor, also known as the neutralising conductor, connects the MET to the PEN conductor in a TN-C-S installation, with the earthing conductor connected to the MET and the earth electrode.
A TN-C-S installation is known as a Neutralised installation.
It is clear that this is what the poster was referring to (but not the original post!).
I am referring to a tncs system not a tnc. We are expected in Ireland to neutralize an installation if we come across a tt system, by the way 30 ohms would not be accepted here a good ze, relying on the general mass of earth to carry fault current is not acceptable here, not sure if the UK supply companies let you do that.
Referring to a tncs not a tns, 30.4 ohms far too high for ze, thats why we are expected to neutralize a tt system here. ze should be quite low, under1 ohm. Sorry for the confusion. If not allowed to do in the uk, let me know, thanks.
That's all well and good if the neutral supply conductor has been earthed at several locations along its length, eg such as found in PME neutrals. It's not such a great idea to willy nilly earth the neutral as and where you come across a TT system.
No it's not allowed in the UK. The only allowable connection to the supplies service neutral is by the DNO, and then generally only when the neutral conductor meets the all the requirements as PEN conductor... Nominally 0.35 ohm but can be higher as stipulated/approved by the local DNO...
fair point, so how do reduce the 30.4 ohms as it is far too high in any circumstances,
thanks for your reply, no system is perfect, it would make sense to allow to use the neutral conductor also as a path for fault current, as the mass of the earth might not be good enough conductor on its own hence 30.4 ohms. in ireland that is what we do in a tt system, in fact we would regard the customer earth electrode as secondary to the neutralizing conductor. also i am not taking away the absolute importance of having an earth electrode in place, if for example the supply neutral if overhead and single ever became open circut. this is only an observation of mine not a rewrite of the rules.
Ah well, there lay's another problem with BS7671!! lol!! They don't give a maximum value, only suggest that a Ra value over 200 ohms is unlikely to be stable!! Far too many actually think that is the maximum level, but they'd be very wrong...
So most totally rely on a 30mA RCD rather than try and reduce the Ra value while the more enlightened, will also install an upfront 100mA S type RCD to cover the possibility of an inoperative 30mA RCD...
There's plenty of threads on this subject in the archives here!! lol!!
good point, it is not a good idea to rely on rcd or similar devices on there own, because as you are aware, nobody ever or seldom tests these units, and if they were expected to trip after many years of inactivity, as i have come across many times doing a rcd trip test, which here for a b type standard is 400 ms max.
I understand that creating your own PME is not great, but the majority of the network these days is PME so what's not clever to do it, call in the board & get it changed it's free & as above the network is mostly PME anyway.
i am not saying anything about the fault at this time just about making the house PME
do not create your own pme if not allowed to do so, by your dso. if the dso will do it for free, good. you will now have as good as possible Ze
remember earthing is all about creating the lowest possible [impedance] path for fault current to reach the supply traffo as quick as possible , so the protective device will open as quickly as possible. [ i know this obvious but no harm in reminding ourselves].
Eng, you feelin ok? You didn't mention "twigs" :49:
First off the majority of UK's LV networks are Not PME at all, the overhead supplies that have been PME'd can be considered as true PME but the underground supplies are far more likely to be TNC-S that are partly or in the process of becoming PME in the true sense of the word and can have a Ze value, say anything from less than 0.35 ohm to over 0.80 ohms or more....
There are several reasons why you shouldn't be making your own N-E connection at the DNO's service head, the available Ze may not be suitable, is one....now you have a think about it and come up with at least one or two more??
Oh and it used to be free, but the privatised DNO's have seen it as another source of income that they can squeeze out of customers. Some still are free but not many, and i'd guess not for too much longer!!
#25 read the post I said call them in it is free & if you were to make your own PME what do you think you would check for exactly the same as the board would do (uk power or whoever sorry not the board anymore) you check the ZE across L/N, if I am doing a CCU change then that would be the first thing I check & if it's a TT I advice them they could get it changed for free. Have a guy who works for uk power as cable jointer / fault finder ect on their network & as he has said many times it is nearly all PME now.
never make your own pme unless you are allowed, its important that the dso has a low enough ze, and if tt ze is too high, call the dso and they may neturalise, i would never recommend using a mechanical device eg rcd, solely to protect from earth faults, its better to have a low ze in the first place.
Unexpected reading between Earth and Neutral
not_shocked_yet,
turnitonagain,
