golfpaul
Hello.
Been asked to add bonding to gas, as British Gas has advised customer gas has no bonding.
Gas meter shows no signs of bonding, cannot see bonding to water either.
They have a shower cu which has a 10mm2 earth to it from the main earthing terminal - no other earth cables leave the MET which leads me to believe that neither gas or water are bonded...however:
With this 10mm2 from the shower connected to the MET, i get 0.00 to gas and 0.00 to water.
With the 10mm2 disconnected, i get a reading of 80v, and tester will not continue with continuity test.
There is a clamp of some sort near the stoptap, with bare cable running through the garage, where it appears to be broken in parts.
Does the gas and water need bonding, seeing as though i get a 0.00 with the shower cu 10mm2 connected to the MET.
And why do i get 80v on shower cu 10mm2?
Ta.
Been asked to add bonding to gas, as British Gas has advised customer gas has no bonding.
Gas meter shows no signs of bonding, cannot see bonding to water either.
They have a shower cu which has a 10mm2 earth to it from the main earthing terminal - no other earth cables leave the MET which leads me to believe that neither gas or water are bonded...however:
With this 10mm2 from the shower connected to the MET, i get 0.00 to gas and 0.00 to water.
With the 10mm2 disconnected, i get a reading of 80v, and tester will not continue with continuity test.
There is a clamp of some sort near the stoptap, with bare cable running through the garage, where it appears to be broken in parts.
Does the gas and water need bonding, seeing as though i get a 0.00 with the shower cu 10mm2 connected to the MET.
And why do i get 80v on shower cu 10mm2?
Ta.