ERRRMMM!!! have i misread all this or is your set-up like this... Service head 3ph tailed to a 200amp fused isolator from which you want to supply a dist' board. If this is the case then how will you be tailing i.e. within trunking , clipped direct etc etc...
Firstly you would have been better just fitting a 3ph dist' board with a front end mccb 200amp rated thus omitting the need for an isolator, this would require 95mm tails if standard stranded and in trunking or 70mm clipped direct, can you pls reaon why you get 50mm?
Your method means because you have fused upstream of the tails you only need a 200amp disconnector as main switch in dist' board, but this will most likely be a much larger than normal switch thus requiring an extension box often supplied all in as a kit, do make sure you select the correct dist' board and that its internal busbars are 200amp rated.
(im on the assumption you've fitted 200amp fuses????)