question a mate of mine who has a few houses, has just had an eicr carried out due to change of occupancy and the electrician has said the earth to gas and water wants up grading to 10mm . problem is the whole house as laminated flooring which posses a big problem for him he tells me . the earthing to water and gas looks to me 4mm but when i carried out an r2 test the reading i got was 0.04 end to end .so in theory does he really need to lift the flooring.
 
is it TNC-S? if so 10mm would be required on a new install and an upgrade recommended on existing install. however, if the existing bonding cables are in good condition with no signs of thermal damage, and your readings are as you stated, then it's a C3 and can be left as is.
 
Why not? The minimum size is 6mm in the regulations with no mention of any allowance for smaller if the resistance is a certain value, therefore the resistance of a main bond smaller than 6mm is irrelevant.

Unless you have a particularly long run and go over the 0.05 Ohms. Daz
 
The 0.05 Ohm recommended maximum. It was a tongue in cheek comment - don't take it too seriously! I'll put a smiley on next time :) Daz
 

Reply to upgrade or not in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
988

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top