hightower
Say you were going to change a CCU, and it is an 80A fuse with 16mm tails (10mm earth). Bonding is in place in 6mm. What would you do with regards the tails and bonding? Been thinking about this scenario all morning and it's bugging me now. I'll walk you through my thinking, would appreciate a mentors thoughts.
Assuming reference method C 16mm is good for 87A according to table 4D1A, so the tails are acceptable.
Now assuming a good Ze of 0.10 and plugging those figures in to the adiabatic:
230/0.10 = 2.3kA
2300 x 2300 x 0.1 = 529000 (sqrt) = 727.32 / 143 = 5.09mm
Assuming a poorer Ze of 0.35:
230/0.35 = 657A
657 x 657 x 1 = 431649 (sqrt) = 657 / 143 = 4.59mm
So my thinking is the earthing conductor is up to scratch with regards adiabatic, and being TNCS would need to be a minimum of 10mm anyway - that's what is installed.
Next, bonding. Table 54.8 states that bonding should be 10mm minimum. We have 6mm installed. Not acceptable.
Now, this is what I think I would do in this situation, but would love to be told if I'm thinking correctly or not by the mentors. If the tails and earthing conductor were in good condition, I would leave them in place and reuse them in the new CCU. If not in a good condition, or if it they were easy to replace (not ripping walls apart) I'd replace them and probably stick 25/16mm tails/earth in - may as well if making a mess anyway?
As for the bonding, I'd upgrade it to 10mm. Now I've seen the arguments for both sides of the story in that if 6mm is installed and shows no sign of thermal damage etc then it can be reused. To me though, it just wouldn't feel right.
So am I thinking along the right lines, that it's okay to reuse the tails etc if they meet the requirements?
And that leads on to a slight change of scenario - everything the same, except a 100A fuse now. I've seen the arguments again that it's okay to use the tails if they show no signs of damage even if they are undersized now.
Assuming reference method C 16mm is good for 87A according to table 4D1A, so the tails are acceptable.
Now assuming a good Ze of 0.10 and plugging those figures in to the adiabatic:
230/0.10 = 2.3kA
2300 x 2300 x 0.1 = 529000 (sqrt) = 727.32 / 143 = 5.09mm
Assuming a poorer Ze of 0.35:
230/0.35 = 657A
657 x 657 x 1 = 431649 (sqrt) = 657 / 143 = 4.59mm
So my thinking is the earthing conductor is up to scratch with regards adiabatic, and being TNCS would need to be a minimum of 10mm anyway - that's what is installed.
Next, bonding. Table 54.8 states that bonding should be 10mm minimum. We have 6mm installed. Not acceptable.
Now, this is what I think I would do in this situation, but would love to be told if I'm thinking correctly or not by the mentors. If the tails and earthing conductor were in good condition, I would leave them in place and reuse them in the new CCU. If not in a good condition, or if it they were easy to replace (not ripping walls apart) I'd replace them and probably stick 25/16mm tails/earth in - may as well if making a mess anyway?
As for the bonding, I'd upgrade it to 10mm. Now I've seen the arguments for both sides of the story in that if 6mm is installed and shows no sign of thermal damage etc then it can be reused. To me though, it just wouldn't feel right.
So am I thinking along the right lines, that it's okay to reuse the tails etc if they meet the requirements?
And that leads on to a slight change of scenario - everything the same, except a 100A fuse now. I've seen the arguments again that it's okay to use the tails if they show no signs of damage even if they are undersized now.