Upgrade tails on CU replacement? | on ElectriciansForums

Discuss Upgrade tails on CU replacement? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 27, 2020
Messages
55
Reaction score
38
Location
uk
Hi. I have my NAPIT first assessment soon and I replaced a CU in a house which has 16mm2 consumer tails in place. I did not upgrade the tails to 25mm2, so my question is should I have upgraded them or am I allowed to leave the existing tails in place?
I do not know the rating of the DNO cut-out fuse
Yes the cut-out does have 100A stamped on the fuse carrier but that means nothing
Installation is 25 years old

Thanks
[automerge]1600593380[/automerge]
Hi. I have my NAPIT first assessment soon and I replaced a CU in a house which has 16mm2 consumer tails in place. I did not upgrade the tails to 25mm2, so my question is should I have upgraded them or am I allowed to leave the existing tails in place?
I do not know the rating of the DNO cut-out fuse
Yes the cut-out does have 100A stamped on the fuse carrier but that means nothing
Installation is 25 years old

Thanks
Also it was a Lewden RCBO board and I brought the cables through the knockout in the rear, am I required to use fire sealant in the rear section?
 
Last edited:
16mm tails will be fine as long as they're not supplying a pot farm. mention to inspector that you've calculated the max load (allowing for diversity) at <80A.

no need for fire sealant unless you have broached a fire barrier.
 
I was generally under the impression that tails need to be updated to 25 on a 100a cut-out , but as tel says 16mm is fine in 99% of domestic situations and imo I would only ever use 16mm if the regs allowed it in all situations

as for fire foam , no you don’t unless it’s a ruddy great big hole in the wall
 
Be prepared to explain the reasons why they are 16mm tails and if you do what Tel says have your diversity calculations ready.
Hole in the back will be ok.
Might be asked if the RCBOs are Type AC or Type A and the reason for the selection.
Did you check all main bonding?
 
Be prepared to explain the reasons why they are 16mm tails and if you do what Tel says have your diversity calculations ready.
Hole in the back will be ok.
Might be asked if the RCBOs are Type AC or Type A and the reason for the selection.
Did you check all main bonding?

out of curiosity what are the fundamental differences between ac & a type rcbos

I believe only some manufacturers make both varieties
 
The problem with the 'type AC' RCD is the current sensing transformer can be saturated quite easily by some DC component and it becomes blind to the AC part. I think some MFT used to use that trick for "no trip" Zs measurements.

Type A should have a bigger transformer and/or different magnetic core type so a "pulsed DC" waveform (i.e. AC & DC combined, say rectified mains) still produces enough of a measurement to fire the RCD trip mechanism. Cost should not be much more than type AC to make this.

I think that 'type B' RCD use a hall-effect sensor instead of a transformer's secondary winding so they can detect a smooth DC fault (as well as AC/pulsed DC), say leakage from a EV battery pack. Unfortunately the cost for parts here is significantly more than A/AC approach, but probably not as much as the catalogue price would suggest, that might be partly due to much lower demand, etc.
 
Last edited:
The problem with the 'type AC' RCD is the current sensing transformer can be saturated quite easily by some DC component and it becomes blind to the AC part. I think some MFT used to use that trick for "no trip" Zs measurements.

Type A should have a bigger transformer and/or different magnetic core type so a "pulsed DC" waveform (i.e. AC & DC combined, say rectified mains) still produces enough of a measurement to fire the RCD trip mechanism. Cost should not be much more than type AC to make this.

I think that 'type B' RCD use a hall-effect sensor instead of a transformer's secondary winding so they can detect a smooth DC fault (as well as AC/pulsed DC), say leakage from a EV battery pack. Unfortunately the cost for parts here is significantly more than A/AC approach, but probably not as much as the catalogue price would suggest, that might be partly due to much lower demand, etc.
Think your pretty spot on with your summery there. Although the price of A Types is now pretty low. Fusebox for example there about 4 quid more for the type A RCBOs. Type Bs are still expensive, up to ÂŁ200 in some manufacturers.
 
I suspect type AC will go fairly soon, as I don't think they are permitted in many EU places now, so no point in making two versions for any new design.

I don't really expect type B to drop massively though as they will only ever be used for things like EV chargers or PV supplies, which at best is going to be something like 10% or less of all applications. Fundamentally they are going to be more complex as well.
 
I suspect type AC will go fairly soon, as I don't think they are permitted in many EU places now, so no point in making two versions for any new design.

I think your right! I did see a snippet of A2 (which is due to go to DPC soon) which Sparkninja put on his instagram, I expect you saw it too!
The wording was something along the lines of,"Type AC rcds can only be used to serve fixed equipment, where it is known the load contains no DC components(see note4)

Examples in note 4 being simple filament lighting and basic electric heating.
 
I don’t believe ACs are used in Europe in many country’s now, they were phased out over the last years for Types As. Frustrates me still when I ask for Type As in wholesalers and they ask me why I fit them when everyone else just sticks ACs in.
Indeed.

But while AC are a couple of quid cheaper they will still be chosen by folks who don't know (or care) about the difference.

Though as said before, I suspect the real risk is small, but growing as more things have DC derived directly from mains used (e.g. washing machine motors).
 
I never understood the use of the AC type in France, when the A type was only a couple of € more, but the AC type is still available, I just wonder if its old stock being run down or they are still being manufactured.
 

Reply to Upgrade tails on CU replacement? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
721
  • Locked
  • Question
I'm not sure where this thread is going or what you are demonstrating is by an electrician or yourself. It doesn't really matter as the forum...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top