E
EastAnglian
ON an EICR today I observed an installation with two properly connected equipotential bonding cables to gas and water services run correctly to the DB. However these two cables were 6 sqmm, not 10sqmm CSA as now required by the Regs.
Its a period property with wattle & daub walls and the route for the EB cables is a pig to upgrade, requiring a route from ground floor to attic and all sorts of other challenges and disruption.
The gas and water services both rise in the kitchen and are about 1m apart on the same wall. Now, if I cross-bond between both services in the kitchen with a 10sq mm cable then to my simple way of looking at this I will end up with a 'single' 12sqmm bonding cable connecting both services (albeit with a short 10mm 'tail'). The cross-bonding would be equipped with the "safety earth - don't remove" label.
Would you agree this is a pragmatic way to meet the regs?
Its a period property with wattle & daub walls and the route for the EB cables is a pig to upgrade, requiring a route from ground floor to attic and all sorts of other challenges and disruption.
The gas and water services both rise in the kitchen and are about 1m apart on the same wall. Now, if I cross-bond between both services in the kitchen with a 10sq mm cable then to my simple way of looking at this I will end up with a 'single' 12sqmm bonding cable connecting both services (albeit with a short 10mm 'tail'). The cross-bonding would be equipped with the "safety earth - don't remove" label.
Would you agree this is a pragmatic way to meet the regs?