HI mate
from measuring the PEFC ( prospective earth fault current )by measuring between line terminal of the supply side of main isolator and the MET at the origin with theMain earthing conductor connected , and the PSCC (prospective short circuit current) at origin between the line terminal and the neutral terminal of the main isolator with the load removed ie all CBs switched off and the main isolator switched off and isolated, the highest of the two is the PFC and should be recorded on the eic under nature of supply parameters and the schedule of test results
the short circuit capacity of the device to be recorded in kA is the maximum the CB can withstand Icn before the CB is unusable and Ics is the service short cicuit capacity which in the case of a BS60898 is the same but not in all cases. The pfc should be less than or equal to the max breaking capacity of the protective device ie for BS 60898 type B 6kA usually for domestic but could be anywhere between 1.5kA and 25kA its marked on the front of the cb or the side of it