SimpleSimon
Hi Guys
Urgently need clarification on something please.
I'm currently sitting in darkness in a shop where for the last 24 hours two phases out of three on the incoming service cable have been blowing within 5 minutes of power being restored. So far I THINK I've narrowed it down to a till point. But heres my confusing situation.
TWO phases blowing- All circuits are single phased equipment EXCEPT an air con unit which was isolated first time the fuses blew by the MCB. Since than it has blown several more times.
So looking at it what would determine two phases blowing at the same time with all single phase equipment in place?? Well the landlord engineers have IR'd the phases to earth and they tell me it's all clear and no problem there.
Next we have a data cabinet with two shop floor till points and a UPS system involved. Now interestingly enough the two till points are spread over the two faulty phases with the data cabinet also being on one of the phases. We've taken a guess at thinking there is a fault with the UPS system as this is what looks like the only thing connecting the till points across two phases. So, we disconnect the UPS entirely and switch on one till and the data cabinet. After a couple of minutes the fuse goes again. So this time I only turn on one till point and leave the data cabinet and other till isolated. Fuse replaced and than again it goes. This was the last time. Now I've unplugged all components from both till point circuits and I'm going to run some tests on the circuits.
My question is this- why is a BS88 63a fuse blowing before C16 MCB? Do BS-88 have higher breaking capacity?
Im going to get my book and study the time curves whilist I wait but I was hoping someone would also be able to give me a quick summary of the reasons as I'm afraid time is against me to keep re-reading the pint s in my book.
Thanks
Simon
Urgently need clarification on something please.
I'm currently sitting in darkness in a shop where for the last 24 hours two phases out of three on the incoming service cable have been blowing within 5 minutes of power being restored. So far I THINK I've narrowed it down to a till point. But heres my confusing situation.
TWO phases blowing- All circuits are single phased equipment EXCEPT an air con unit which was isolated first time the fuses blew by the MCB. Since than it has blown several more times.
So looking at it what would determine two phases blowing at the same time with all single phase equipment in place?? Well the landlord engineers have IR'd the phases to earth and they tell me it's all clear and no problem there.
Next we have a data cabinet with two shop floor till points and a UPS system involved. Now interestingly enough the two till points are spread over the two faulty phases with the data cabinet also being on one of the phases. We've taken a guess at thinking there is a fault with the UPS system as this is what looks like the only thing connecting the till points across two phases. So, we disconnect the UPS entirely and switch on one till and the data cabinet. After a couple of minutes the fuse goes again. So this time I only turn on one till point and leave the data cabinet and other till isolated. Fuse replaced and than again it goes. This was the last time. Now I've unplugged all components from both till point circuits and I'm going to run some tests on the circuits.
My question is this- why is a BS88 63a fuse blowing before C16 MCB? Do BS-88 have higher breaking capacity?
Im going to get my book and study the time curves whilist I wait but I was hoping someone would also be able to give me a quick summary of the reasons as I'm afraid time is against me to keep re-reading the pint s in my book.
Thanks
Simon