Hi Guys. I need to get a report done by 2pm. Sorry if this is a lame question but I am having thoughts on the main switch rating. Its TNC-S. 100amp 1361. Small house. Immersion removed and single socket installed, one socket ring, one cooker radial, two lighting radials. All on 63a Main switch 30mA RCD ok so far BUT 6 years ago they have had a 9.5kW shower fitted to this same consumer unit. Im thinking the 63a not enough?
 
any signs of the RCD terminals overheating? to overload a 63A RCD/main switch, they'd need the shower, cooker, and a couple of 3kW heaters all on at the same time. forget it. you could, if concerned, make a note in the comments section recommending an upgradeto 80A, but i'd not bother.
 
Hi,
Most people on here will tell you, pulling a constant 60A + just isn't going to happen. Do your Diversity checks, see what you come up with, if you are still concerned then maybe reccomend an 80A. After all it's an EICR, use your knowledge of the said Installation and make a decision either way.

Regards.
 
Hi Guys. I need to get a report done by 2pm. Sorry if this is a lame question but I am having thoughts on the main switch rating. Its TNC-S. 100amp 1361. Small house. Immersion removed and single socket installed, one socket ring, one cooker radial, two lighting radials. All on 63a Main switch 30mA RCD ok so far BUT 6 years ago they have had a 9.5kW shower fitted to this same consumer unit. Im thinking the 63a not enough?


Think you answered your own question here!! lol!! 6 YEARS and no mention from you of any signs of overloading or terminals burning to this RCD!! Average 3 bed house you'll be lucky to see 45-50A for more than a few minutes, most of the time you'll be in single to low double figures!!

So do you have a problem in this instance?? ...NO!! lol!!
 

Reply to Urgent Please :: 63a Main RCD Switch on EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
Good point, they do look a bit 6mm-ish when you mention it, and that is not going to last long enough for a D63 to trip! It might, on a good day...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top