Yes that's exactly what I'm suggesting.
To my mind, a conductor can be both a bonding and a CPC at the same time.
Just waiting for someone to disagree and state that the 10mm² has to be a single condutor, or that both conductors have to have the same CSA or something.
 
Last edited by a moderator:
Yes that's exactly what I'm suggesting.
To my mind, a conductor can be both a bonding and a CPC at the same time.
Just waiting for someone to disagree and state that the 10mm² has to be a single condutor, or that both conductors have to have the same CSA or something.


Lets have your reasoning then.
 
Thinking that the protective bonding conductor may have to carry large fault current in the event of failed incoming neutral or neutral of the distribution circuit. In this case, the distribution circuit is protected by RCBO so it should trip anyway?
 
There has been research and testing provided to the "industry" that goes along with the idea that the fault current will be shared acceptably by an internal core & the SWA, & / or an external cpc, the internal core & the SWA.
So you can do any of the above.
Also if you check GN1 you will get armour csa's for compliance with table 54.7, from this you should be able to assess your suitability.

Also you can use the adiabatic to size bonding conductors.
 
I was assuming that the 6mm² CPC was adequately sized.
With PME, the CSA is chosen so the conductor can withstand diverted neutral currents for long periods of time, rather than earth fault currents for short periods of time.


My view is that we cannot guarantee how much fault current will flow in which conductor so one should be sized to carry out the function solely.
 
There has been research and testing provided to the "industry" that goes along with the idea that the fault current will be shared acceptably by an internal core & the SWA, & / or an external cpc, the internal core & the SWA.
So you can do any of the above.
Also if you check GN1 you will get armour csa's for compliance with table 54.7, from this you should be able to assess your suitability.

Also you can use the adiabatic to size bonding conductors.

Not sure about being able to size main bonding by adaibatic with TNC-S paul? i think your allowed to on TNS & TT.
 
My view is that we cannot guarantee how much fault current will flow in which conductor so one should be sized to carry out the function solely.
Both as I understand it are sized adequately to carry the fault current.
The armour apparently is equivalent to 15mm2, with regards to k2/k1.
It's just the conductance equivalence that doesn't meet the requirements.
 
Lenny,
I understand your point, but one of the major players has commissioned research, and it has been done & published, it states that you are fine with the scenario I describe.
The research is on the internet somewhere, I think I also have it on my disk, but I can't look now sorry guys.
Wife's car has just broken down, why when we are skint!
Running on 3 cyls by the look of it, that's only half the engine, so big problems.
May be back later, or if I'm not around for a few days, sorry but I may be doing car mechanic type things!!!
 

Reply to Use of SWA armour as protective bonding conductor? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

totally agree
Replies
12
Views
1K
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top