Hi, doing some work in a bathroom at the moment - just on the lighting circuit. Ext fan & ELV lights. As the house has no RCD protection at all I'm obliged to add it. All circuits are split between two 8way consumer units, each with main switch and MCBs. My options for adding RCD protection are either:

1. Just replace the lighting MCB with an RCBO - my preferred option, although I don't think the CU will accommodate the extra height of the RCBO.

2. Add an RCD in it's own enclosure in front of the CU which includes the lighting MCB. Not ideal as there'll be a lot more testing of the other circuits involved to avoid the risk of nuisance tripping from circuits I've not touched. Also, no other point of isolation so will have to pull the fuse (or get DNO in to isolate:rolleyes:)

3. Alternatively, I could replace the main switch with an 80A RCD, like you would see in many 16th edition CUs. I would put a MAIN SWITCH label under it.

Any reason why option 3 wouldn't be proper? It seems a bit regressive, but would be the neatest solution if the RCBO doesn't fit..
 
An RCD should not be used as a main switch. 314.2

16th edition split boards have a main switch controlling all circuits & an RCD controlling split side.
 
Last edited:
Okay, I had a suspicion this was the case, but thanks for pointing out the relevant reg. Sure I'd seen boards where RCD was used as main switch - maybe my imagination!
Thanks a lot sintra, much appreciated.
 
In the late 80's/ early 90's a few housing developers installed CU's with an RCD as the main switch, I don't know how long it was done for, but I have seen it many, many times in properties built around that time.
 

Reply to Use RCD as main switch? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
844
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
967

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
792
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
952

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top