Use RCD as on/off switch | on ElectriciansForums
Discuss Use RCD as on/off switch in the UK Electrical Forum area at ElectriciansForums.net
West Sussex
Is it permissible to use the reset + test buttons of an RCD plug adapter as on/off buttons for a 10A load?
I have a 2000W power saw which I want to switch on and off at the socket under load, ie. the tool's own switch will be permanently on. (The details are un-important.)
I have an extension cable with unswitched sockets, and want to use an RCD for safety. I don't really want to add a third component in the form of a switched multi socket adapter, and in any case like the idea of quick, colour-coded push-buttons to operate the saw.
Are the reset & test buttons suitable for such load switching?
No as they are designed as test switches and not for functional switching. They would fail eventually, probably quite quickly with a 10 amp load.
As above, a 2kW power saw will have a high inrush current so it will quickly burn the RCD contacts out.
Ideally you are looking for a "Direct On Line" starter such as this:
https://uk.rs-online.com/web/p/dol-star-delta-starters/9094079/
Most 3-phase starters can be wired for single phase, they are basically a 3-pole contactor and start/stop buttons to allow the windings of the contactor the be energised and de-energised. Also they release automatically on power fail, so it the mains returns after a fault the motor does not burst in to life!
The good thing about an NVR is they switch off automatically if you get a power failure, in as a trip of the MCB or RCD, so when you switch the power back on the unit does not start up by itself, you have to reset the switch, I have them on all my large workshop tools, even the extractor.
Reply to Use RCD as on/off switch in the UK Electrical Forum area at ElectriciansForums.net
L
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Thanks for the advice.