I added an additionl socket to the existing ring in a block of flats the other day and there was no seperate earth conductor,the conduit was acting as it. I moved the circuit to a new consumer unit so the ring was now protected by a RCD. When it comes to filling out the test schedule what do I enter in the R1+R2 column. I assume you enter NAis this correct and if not whats the next move.
 
You must have an R1+R2 value. Saying N/A implies that it isn't required or doesn't apply to this circuit. It does. The procedure is slightly different but you should get a measurement.

Without it, you're saying there's a problem.
 
You measue the R1 + R1 as per usual and make a not on the certificate that the CPC function is being performed by the earthed metallis conduit.
You need to confirm that this is the case and that there is a CPC connectign the back box/ installation box terminal in the wall to the earth terminal on the face plate of the accessory.
It would be a good idea to put a lable on the consumer unit stating that the conduit is used as the CPC and must not be compromised.
This is a acceptable way of prociding a cpc, not to mention the mechanical protection for the cables.
 

Reply to Using a conduit sysem as the CPC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
264
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Crimp or Wago inline connector, my preference would be Wago push fit...
Replies
1
Views
246
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top