I want to use the armour as my CPC but need to check it complies. The cable will be run from a SP Distribution panel to CU.
As per Selection and Erection Guidance Note 1 table D10a I can see a 10mm XLPE SWA requires a 31.1mm csa to comply, but only has 26mm on 2-core.
20171231_114229828_iOS.jpg - https://1drv.ms/u/s!ApQQCRGg1ka_gvxxrqQ0QslTR-xaHg
So the only way I might be able to use this is to calculate using adiabatic equation.
Is my calculation correct?
Voltage = 230v
Ze = 0.09 (to be verified, taken from old EIC)
I = 230/0.09 = 2,555A
I2 = 6,528,025
t = (Fig 3A1, 100A BS1361 Type 2a > 1,450A) = 0.1s
I2 x t (6,528,025 x 0.1) = 652,802
sq Root 652,802 = 807
k = 46 (TABLE 54.4 steel)
S = 807/46 = 17mm
So looking at table D10a above we can see 10mm XLPE SWA has csa of 26mm, but as I only need 17.5mm I will be fine ?
On a similar note, Table 4E4A advises 10mm 2-core SWA capacity in ducting is 71A
20171231_140220034_iOS.jpg - https://1drv.ms/i/s!ApQQCRGg1ka_gvxzxVXvCVCdScy83Q
But manufacturers notes say in duct I can run their cable up to 89A, I assume in this instance I could use manufacturers notes over Table 4E4A as Table 4E4A is only generic ?
SWA Capacity.pdf - https://1drv.ms/b/s!ApQQCRGg1ka_gvxyaNUN1GXpn1Ob8w
In reality I'll protect with either 50A or 63A MCB, but it's possible I might want to run at 80A in the future. Now I know the cable spec so I know it's safe; I can also leave cable spec with EIC, but is there anything else I should do to prevent another electrician in the future condemning the cable?
As per Selection and Erection Guidance Note 1 table D10a I can see a 10mm XLPE SWA requires a 31.1mm csa to comply, but only has 26mm on 2-core.
20171231_114229828_iOS.jpg - https://1drv.ms/u/s!ApQQCRGg1ka_gvxxrqQ0QslTR-xaHg
So the only way I might be able to use this is to calculate using adiabatic equation.
Is my calculation correct?
Voltage = 230v
Ze = 0.09 (to be verified, taken from old EIC)
I = 230/0.09 = 2,555A
I2 = 6,528,025
t = (Fig 3A1, 100A BS1361 Type 2a > 1,450A) = 0.1s
I2 x t (6,528,025 x 0.1) = 652,802
sq Root 652,802 = 807
k = 46 (TABLE 54.4 steel)
S = 807/46 = 17mm
So looking at table D10a above we can see 10mm XLPE SWA has csa of 26mm, but as I only need 17.5mm I will be fine ?
On a similar note, Table 4E4A advises 10mm 2-core SWA capacity in ducting is 71A
20171231_140220034_iOS.jpg - https://1drv.ms/i/s!ApQQCRGg1ka_gvxzxVXvCVCdScy83Q
But manufacturers notes say in duct I can run their cable up to 89A, I assume in this instance I could use manufacturers notes over Table 4E4A as Table 4E4A is only generic ?
SWA Capacity.pdf - https://1drv.ms/b/s!ApQQCRGg1ka_gvxyaNUN1GXpn1Ob8w
In reality I'll protect with either 50A or 63A MCB, but it's possible I might want to run at 80A in the future. Now I know the cable spec so I know it's safe; I can also leave cable spec with EIC, but is there anything else I should do to prevent another electrician in the future condemning the cable?